by HotLine1 - 04/23/24 02:17 PM
0 members (), 231 guests, and 11 robots.
#79219 12/07/01 01:42 PM
mdsmith Offline OP
When you install 120V, single phase circuits in a raceway, each with a separate neutral, do you count the neutrals when applying the provisions of 310.15(B)(2)(a)? or does 310.15(B)(4)(a) apply to this situation?
#79220 12/07/01 02:03 PM
Each neutral carries the same current at the associated phase conductor and therefore must be counted as current carrying conductors.
#79221 12/07/01 06:43 PM
In a word... yes. If you have a shared neutral on a single phase multiwire circuit it would not count.
#79222 12/08/01 08:47 AM
Steve,
Isn't that on linear loads?
Non-linear loads using a multiwire method ( N-A-B-C ), the neutral is considered a current carrying conductor. 220-22 FPN#2, 310-15(b)(4)(c).
#79223 12/09/01 01:10 AM
Absolutely. Each neut carries the full load.
[This message has been edited by electure (edited 12-09-2001).]