by HotLine1 - 04/23/24 02:17 PM
0 members (), 231 guests, and 11 robots.
#78911 11/08/01 06:50 PM
Can anyone tell me what are the listed cables with acceptable ground return paths are. As it is referred to in 517.13.
Haven't received my copy of 2002 yet and I have to plan installations for the year year.
#78912 11/11/01 09:23 AM
The Code does not list cables as being approved or not. It only (517.13) requires that:
"The metal raceway system, or cable armor, or sheath assembly shall itself qualify as an equipment grounding return path in accordance with 250.118."
The cable's listing is what will determine its acceptability
Although they mention A/C, M/C, & M/I cable, the only one I know of is A/C for your useage.
This is nearly a repeat of the Q you already asked in another section of the BB.
Check there [Linked Image]
[This message has been edited by electure (edited 11-11-2001).]
#78913 11/11/01 10:04 AM
2002 NEC 250.118 (11) Type MC cable where listed and identified for grounding in accordance with the following:
a. The combined metallic sheath and grounding conductor of interlocked metal tape type MC cable
b. The metallic sheath or the combined metallic sheath and grounding conductors of the smooth or corrugated tube type MC cable
[This message has been edited by Joe Tedesco (edited 11-11-2001).]
#78914 11/11/01 10:06 AM
lemme see,
the only real 250.118 change in 02' is 250.118(1)
A copper, aluminum, or copper clad aluminum conductor.......
#78915 11/11/01 10:53 AM
Be sure to check with the local AHJ as to what edition of the Code they are using before you incorporate any 2002 changes.
Many of them in my area are still basing everything on the '96 Code!
#78916 11/11/01 12:35 PM
Joe,
Just so everyone understands, the combined metallic sheath and the grounding conductor of the interlocking armor type MC cable does not meet the requirement in 517.13.
don(resqcapt19)
#78917 11/11/01 04:58 PM
Here is the exact reference from the new 2002 NEC. What part of this is not clear or understood?
And here is what the 2002 NEC says in 250.118 (11) Type MC cable where listed and identified for grounding in accordance with the following:
#78918 11/11/01 05:17 PM
Joe,
My point is that MC cable that is listed as an EGC per 250.118(11)(a) is not suitable for 517.13 installations because the sheath istself does not qualify as an EGC. It only qualifies when combined with the internal grounding conductor, and therefore does not meet the requirements of 517.13.
#78919 11/11/01 06:29 PM
Joe,
Do you know a company that has type MC or MI Cable that meets the requirements? (Come on, now!) What part don't you understand?
My concern is that if Mr Gardiner specs a freak, it will be a long lead-time item, and will not be acceptable when his EC gets it.
Use AFC's type AC-HCF (as Nick said) or an approved equal, and you can put it to bed.
#78920 11/11/01 07:15 PM
Look here:
http://www.afcweb.com/table2.html
http://www.afcweb.com/fieldhcf.htm
Seems like MC cable is also approved for Fire Alarms.