ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 530 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#78833 10/27/01 10:31 PM
Joined: Jul 2001
Posts: 6
L
lousen Offline OP
Junior Member
Does generator supply entering bldg. underground require a disconnect in bldg? Gen. is 80 feet from bldg.Gen. load 200kva at 208v.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#78834 10/28/01 07:20 AM
Joined: Oct 2000
Posts: 5,392
S
Member
Hi lousen!~
good Q
445.18 requires a disco for a genny, but does not specify where...
225-32, general rule , requires a disco. ex#1 could be applied.
If i'm reading this right (part 2 of 225) it matters if the genny serves the outbuilding or not.
others may clarify this better than I
[Linked Image]

#78835 10/28/01 12:11 PM
Joined: Aug 2001
Posts: 599
N
Member
As a general rule yes. See 225-31. As Sparky stated Ex #1 in 225-32 could be applied but this would have to be acceptable to the AHJ. I don’t believe many would be inclined to accept this.

#78836 10/28/01 07:33 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Lousen,
can you give us more info here? what is the genny used for? etc..
[Linked Image]

#78837 10/28/01 11:03 PM
Joined: Jul 2001
Posts: 6
L
lousen Offline OP
Junior Member
Gen.set mentioned before supplys single owner nursing home.If I open main service disconnect in basement in a fire emergency, Gen. set kicks in.which means power is back on. Nearest disconnect is at Gen. set-80 feet away.This installation is completed but not inspected.

#78838 10/29/01 07:40 AM
Joined: Aug 2001
Posts: 16
G
Member
The answer is yes you do need a disconnect within sight. Check out 700.12(B)(6) in the 2002 NEC.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5