ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 520 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 3 1 2 3
Joined: Apr 2001
Posts: 449
F
Member
When I calculate the load for a new custom home I use 5va per sqft. It has been my experience with custom homes that "designer" people the homeowners hire like to add lots of different, elaborate "mood" lighting. Not to mention over-the-top accent lighting outside on the house and landscape. I had one house a few years ago that I cut too close for my liking at 5va. Then 2 years after they were in the house they wanted to pitch the gas furnace and convert to geo-thermal w/electric heat bank back-up. Service upgrade on a 2 year-old custom home!

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

A
Anonymous
Unregistered
>Many older properties were wired with only one 5A branch for lighting.
Dare I ask what wire size was used?

Joined: Aug 2001
Posts: 7,520
P
Member
Quote
Originally posted by Dspark:
>Dare I ask what wire size was used?

Originally, it was almost always 1/.044 size (i.e. a single-strand 0.044 in. diameter). From 1970 the metric equivalent is 1 sq. mm. Both are just a fraction larger than #18 AWG.

Joined: Oct 2000
Posts: 5,392
S
Member
hmmm,
i'd probably have thought it to be doorbell wire
[Linked Image]

Joined: Aug 2001
Posts: 7,520
P
Member
Hehe...

The metric size cables are standardized right across Europe now, but in many other countries they specify 1.5 sq. mm as the smallest to be used. That's about 15% larger than #16.

Joined: Jan 2001
Posts: 75
G
Member
Haven't the slightest idea of your smallest standard Over-Current-Protection Device (OCPD), but if 15 Amps, then at 220 volts it would not likely be overloaded, just mechanical protection is needed ????

Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
I can empathise with your concerns and frustrations to the Residential load / service calcs.
Looking at the complete picture, who could have imagined in 1970 that the average house would have so much stuff!
No one would have even expected so many Houses to have 3+ Televisions, Hot Tubs / Spas, Tons of Deco and Task lighting, Increased variety of Small Appliances, Computers in a Home [ENIAC at a House!!! joke], window AC units, and so on.

The real kicker is the concept of "The All-Electric House" in the 1950s, along with increased NEC minimum circuits and grounding in the 1950 - 1960 time period. This must have been a drastic change to Residential load and service calcs than the preceeding time periods [1930 - 1940].
Someone must have been aware that the Residential loads have and will change over time!

Time periods:

1930 - 1940: Simple Incandescent lighting, minimal kitchen appliances, one Radio, very few Television sets owned, very few general purpose receptacles are needed.

1950 - 1960: All-Electric cooking appliances, Central Air, Forced Air heating, Televisions becoming more common, more general purpose receptacle are needed, grounded receptacles in Kitchens, Bathrooms and exterior.

1970 - 1979: More specific circuitry requirements, GFCI's for Bathrooms, etc.

1980 - 1989: Increase in Kitchen loads, more TVs and electronic equipment, people begin to buy Spas and Hot Tubs, more swimming pools, home workshops become more common, garage door openers more common, GFCI's in Garages and outdoor locations, etc.

1990 - 1999: Interior deco and task lighting accelerates, more types of Kitchen appliances and Kitchen layout styles, more home workshops, more Spas and Hot Tubs, Home Computers becoming very common, increasing HVAC installs, Central Vacuum systems becoming more common, exterior spec / deco lighting becomes more common, every room has a TV set plus an Audio system [almost every room!], high power blow dryers are used by almost every household, increasing "DIY'ers" and Contractor based room additions / remodels / other alterations, more swimming pools, GFCI's required in Kitchens or other locations within 6' of sinks [I think that's the distance.?], Dedicated circuit[s] for Bathrooms, etc.

2000: >75% of Homes in North America have at least one PC, Advanced ["High Tech"] systems - such as Audio / Video, Lighting control and other equipment control,- become more widely used, spec type lighting increases, Kitchen appliances continue to become larger variety and more affordable, pending the 2002 NEC's requirements for AFCI dedicated circuit[s], Spas and Hot Tubs holding steady, Home improvement / Remodel / Addition / Alteration projects continue, Home Workshops / Home Based Businesses continue, HVAC systems, swimming pools, increased requests for ample or additional general purpose receptacles, and so on.

2002 - 2010: Who knows???

A few factors have been responsible for a decrease in consumed Electrical Power [KWHs], such as the Deregulation situations here in California, plus the Mandatory Energy Conservation Standards [AKA Title 24, part 6, Chapter 1 - Energy Efficiency Standards] which are the State wide default code[s] requirements throughout California. These factors could influence the future load demands in the typical Residential occupancy.

FYI: A little history on California's Energy Conservation standards [CBC, CMC, CPC, CEC]:

The OPEC oil embargo of 1973 brought the U.S. into the infamous "Energy Crisis". Most everyone on this board remembers that situation. Also, most everyone here has heard of the Smog problem in Southern California.
These two factors were the primary influence for the California State Legislature to create the California Energy Commission in 1974, to deal with energy-related issues and adopt condervation standards for new buildings.

The Subchapters involved are:

Subchapter 1: General Provisions - All Occupancies.
Subchapter 2:Mandatory - Equipment Manufacture and installation of systems and equipment.
Subchapter 3: Mandatory - Mechanical systems and equipment.
Subchapter 4: Mandatory - Lighting systems and equipment.
Subchapter 5: Performance and prescriptive approaches [the calcs and compliance sheets themselves].
Subchapter 6: Special topics and repairs.

These standards apply to the "Envelope" [Framing, Glazing, Insulation and Foundation], Mechanical, Plumbing and Electrical Lighting for both Residential and Non-Residential occupancies.

The first generation of Title 24, part 6 was 1978 [2/78], which involved Residential occupancies (Including Hotels and High-Rise Apartments). The first generation Non-Residential followed soon after in 1978.
After this, newer compliance standards were introduced in 1983, 1984, 1987, 1988, 1992, 1995 and 1999 - with the latest revision this year [2001].

The goal in 1978 was to decrease the level of Electrical Power Consumption [KWHs] so that by 2009, the standards would save more energy than seven [7] average fossil fuel burning power plants could produce.

The last Energy Calc I did was under the 1999 standards. At that time, the amount of power saved, plus the reduction in consumed energy eliminated the need of around 6 average power plants! Smog levels and Acid rain was dramatically reduced.
All this got completely screwed from Deregulation!

Current Title 24 requirements for Residential Lighting calls for Energy Efficient lighting [40 lumens per watt minimum] used in Bathrooms and Kitchens [as "Primary" lighting source], plus for exterior lighting at exterior doors.
Insulation, Glazing and similar requirements increase the building's thermal conductivity resistance, which results in lower HVAC consumption.

Electric Resistance type heating used with HVAC systems is not allowed. Heating is either fuel [gas, etc.], or heat pumps.

Water heating for over 25 gallons may not be Resistance Electric. If Recirculating pumps are used, they must be controlled so they are "off" during non-use periods [not running while people are sleeping or away!].

For Non-Residential occupancies, there's a vast amount required for HVAC, Plumbing and Envelope.

For Lighting, there's 4 methods of calculation - but the maximum lighting power levels fall less than what you would see listed in the NEC article 220.
However, the NEC value is always used for calculations of service sizes, as covered in article 220 - unless the designed loads are higher than NEC minimums.

Example:
Commercial Bank Branch:
CEC [Title 24] maximum lighting power= 1.6 watts per square foot.
NEC load calcs= 3.5 VA per square foot [general lighting load].

The installed lighting equipment cannot exceed the maximum lighting power of 1.6 watts per square foot [actual and total consumed watts of lighting fixtures is figured instead of VA], but the service and feeders are calced using 3.5 VA per square foot.

Lighting equipment is influenced by these standards, so are lighting controls.

These standards will continue to increase in the future, so this will have resulting effects on new / remodel / addition projects and corresponding circuitry.


Well, I hope this message was enlightening to everyone.

Scott SET

P.S. edits to as many typo's and spelling errors I could find.
Iee R knot sutch ae gud spelor, axtuly mie spelyng sux! [Linked Image]
[translation available upon request [Linked Image]]
S.E.T.

[This message has been edited by Scott35 (edited 10-08-2001).]


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Aug 2001
Posts: 7,520
P
Member
Glenn:

The smallest OCPD generally used in domestic panels is 5A for lighting circuits, the next fuse size being 15A, but C/Bs are also available in 10A. Many new ranges of breakers are actually 6A instead of 5A due to the adoption of European stadards.

Twin-&-earth (like Romex) 1 sq. mm can be run the same way as the larger sizes, with no special requirements.

Joined: Oct 2000
Posts: 5,392
S
Member
All this got completely screwed from Deregulation!

It did???
[Linked Image]

Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Steve,

I say this because now California is racing to construct 15 new power plants - 4 or 5 of them already in operation, all due to the rolling blackouts and high prices per KWH / MWH to power generating companies.
These are the results we have been facing in California from Deregulation.

In 1999, the Energy Standards reduced KWH consumption equal to the output of 6 average fossil fuel burning power plants.
This considerably reduced the output power demands on power plants, loss of power [blackouts] to customers, pollution and acid rain, reliance on more fossil fuels, allowed more conservation of fossil fuels, even reduced U-239 waste disposal levels! [highly radioactive U-238 spent, or used fuel after reactions].
Now California is building more power plants which will no doubt be running at least 50% output load continuously.

That's what I mean by everything has been screwed by Deregulation.

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Page 2 of 3 1 2 3

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5