ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
2 members (gfretwell, Scott35), 527 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#78363 09/11/01 07:08 AM
Joined: Dec 2000
Posts: 4,294
Member
In one of our municipalities, city code requires that a torque test be performed in front of the inspector (all panel and EXO terminations). OK, no biggy.

The same city requires a neutral to ground fault test. The building ground is disconnected from the neutral connection, and a test for continuity from load neutral to ground is performed. Kind of a pain in the ***, but it seems like a good idea.

Anybody else ever run into this? It's a first for me.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#78364 09/11/01 07:27 AM
Joined: Oct 2000
Posts: 5,392
S
Member
??what is, or how is it tested?, i'm drawin' a blank here Scott......
[Linked Image]

#78365 09/11/01 07:47 AM
Joined: Mar 2001
Posts: 2,056
R
Member
EXO=Disconnect?

#78366 09/11/01 08:07 AM
Joined: Aug 2001
Posts: 599
N
Member
This wouldn't be Huntington Beach would it?!

#78367 09/12/01 08:04 AM
Joined: Dec 2000
Posts: 4,294
Member
Nick,
Right-ee-o, Surf City USA. Is this the only place where this is done? I'll add some more of their oddities for the other guys.
1.Appliances hardwired (GD, DW, etc). Disco means mounted where you'd normally put your recp.
2.PVC outdoors(or EMT, GRC painted with $60 per gallon marine paint) Go down the street a couple of blocks to Newport Beach, and they'll lynch you for using PVC on the roof.
3. 2x4 fluorescents in T-bar, 4 support wires to structure, 4 screws to grid. Downlights in T-bar 2 wires to structure, 4 screws.

Steve,
The process is to remove the grounding connection from the service neutral (I had a hot service, so was allowed to remove the neutral feeder conductors from their lugs in the panels, on a resi service, you take all the branch circuit neuts off and test them individually)
A continuity check is then taken from the neutral bar (or branch circ cond) to ground. You shouldn't have continuity. If you do, there is a fault someplace (screw through cable, etc). It would show up on an ungrounded conductor by a tripped C/B, but on a neutral, would never be found without this test. Seems like a real good idea to me.
I just have never heard of it elsewhere
(HB once had an inspector that thought "outside the box")

#78368 09/12/01 04:17 PM
Joined: Aug 2001
Posts: 7,520
P
Member
I hadn't really thought about this before, but with your common neutral/ground busbar, I guess to find a short on a branch circuit you would have to test before both are connected to the bar.

In the U.K., we always have separate neutral and ground busbars, even in places where PME is used and the ground is bonded to the incoming neutral.

It's standard practice on a new installation to do two final megger tests:

1. All switches closed, bulbs removed, appliances unplugged etc. Test between hot & neutral with all fuses in/breakers closed.

2. Temporarily strap hot to neutral and megger between them and the ground busbar. It's also acceptable to do two separate tests: hot to ground & neutral to ground.

We don't even need to disconnect any main cables for these tests on domestic work, because our main switches are D.P. and open the neutral as well.

#78369 09/12/01 10:47 PM
Joined: Aug 2001
Posts: 599
N
Member
Quote
Originally posted by electure:
Nick,
Right-ee-o, Surf City USA. Is this the only place where this is done?

This is the only place I know of. I have never worked there but have heard all the complaining of co-workers that have. We do a lot of work there especially at Bowing. I think the neutral to ground test is a good idea. They do get a little carried away sometimes. One example: Parallel conductors. My superintendent was called by a Huntington Beach inspector because the CONDUITSwere not the same length. They knew the city was very particular about having the conductors exactly the same length(absolutely no variance) so they laid them on the floor, cut them EXACTLY the same length and then installed them without cutting them. The inspector would not pass the installation because the conduits were different lengths.

#78370 09/13/01 02:31 AM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
I also had the test done in Huntington Beach, along with a few other areas. John Childress from Simi Valley DBS is one that prefers this test.
It's a great idea to check it after the other trades have finished, just to make sure there's no re-grounded grounded conductors! [what a redundant statement [Linked Image]].
Not only that, but the "Neutral Disconnect Link" which service type switch gear has, gets to be used finally!

One other thing about Huntington Beach was penetration of the methane barrier under concrete slabs. I guess that there's an increasing amount of methane gas being pushed inland from the ocean. There's sure a lot of oil pumps in that area!!!

We saw cutted the existing slab to install floor boxes and stubs for teller line [bank branch project] and the Building Department was very concerned with us penetrating the methane barrier.

FYI: The SCE feeder conduits, along with the Telco riser duct to the MPOE were sealed like a gas station's conduits would be. Very rarely see that done!

Scott [electure],
We had to paint the heck out of any underground/underfloor ducts, conduits and boxes too! Once again, the methane situation must be the reason for this.
The Fire Sprinkler's feed [from street to the PIV inside building] was also required to be painted this way.
Wonder if the Landscapers' had to treat their irrigation lines??? [Linked Image] - It's possible! I could see methane being able to penetrate the PVC, then enter the irrigation lines and concentrate.

There's a few other AHJ's that want Disposals, Dishwashers, and the like to be hardwired [flex whips]. City / County of LA is one, and I think that Azusa does too. Seems that San Diego is another.

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
#78371 09/13/01 09:45 PM
Joined: Jun 2001
Posts: 7
S
Junior Member
I had a Calif State Mobile Home inspector do this on a mobile I replaced the subpanel in. It showed continuity between the N & G. On further investigation the water heater had the N & G tied together.

#78372 09/14/01 06:41 PM
Joined: Oct 2000
Posts: 5,392
S
Member
!!DING !! okay i got it, thanks
[Linked Image]
come to think of it, not a bad idea for any power quailty concerns either....


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5