#78264 09/01/01 04:27 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
I got a call yesterday to re-do a service upgrade(someone elses)that failed inspection due to 10-12' distance between entrance and Service Panel. The inspector didn't seem to mind that--
1) Service Entrance is 200 amp SE cable buried in 2" PVC from pole-mounted meter socket 30' away.
2) PVC is buried 6-8" deep. Enters below grade. Pokes out in crawl space as cable (no pipe).

Owners suggestion-
1)He will dig new 18"(O.K. with PVC)trench to closer proximity of Panel(2-3').
2)Re-route conduit. Re-use SE Cable.
3)Keep entrance point underground.

I'm thinking no SE Cable underground, even in conduit.
Install new run of USE.
Keep conduit to reduce burial depth from 24" to 18".

Question-
I have only ever installed USE as single conductors. Is multi-conductor USE available as a covered assembly that, when I enter the building, I can run exposed 2-3' to the panel?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#78265 09/01/01 05:19 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Redsy;
I only know of triplex, and some quadriplex USE, no outer covering....

#78266 09/01/01 05:51 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
The penetration to the basement will be close to the panel and if I pipe it, there won't be a lot of room to work 2" fittings. Maybe I'll hit the back of a j-box, and switch(splice)to SE there.

#78267 09/01/01 06:05 PM
Joined: Apr 2001
Posts: 507
G
Member
Quote
Originally posted by Redsy:
The penetration to the basement will be close to the panel and if I pipe it, there won't be a lot of room to work 2" fittings. Maybe I'll hit the back of a j-box, and switch(splice)to SE there.

I know it probably won't be easy to get the conduit in, but I would not install a splice box in the SE conductors. I know that the code allows it now.....but I think that it's still a poor practice.

Run the conduit all the way to the panel. You'll sleep better.

GJ

#78268 09/01/01 07:42 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Can you arrange for a stub of pipe directly into the back of the panel?

#78269 09/01/01 11:09 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
Quote
Originally posted by sparky:
Can you arrange for a stub of pipe directly into the back of the panel?
Good idea! Maybe, but a pain in the you-know-what. The top would be too high with regard to the burial depth. The bottom would be so low as to require the depth to be increased by about 10" at the penetration point. I guess I could slope the last few feet of pipe prior to the penetration.And I'll have to swing the panel out of the way, but it still might be the least aggravating way to go.(Glad I thought of it! [Linked Image])

#78270 09/02/01 06:10 AM
Joined: Oct 2000
Posts: 5,392
S
Member
hey great! I hope it works. just be sure and stuff a pack of dux seal in it so it does'nt let h20 into your panel....

#78271 09/02/01 10:11 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Question,

Would it be allowed to strip the jacket from the SE cable that's in the conduit? And the conduit pokes into the crawlspace with a Female connector on the end and SE cable connector, so it runs as SE to the panel?

What do you think? What would the objections (if any) be?

Bill


Bill
#78272 09/02/01 10:36 AM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
What about this buiness of running SE in the buried PVC. Bad thing, not approved for bvurial. Correct? This was a big(full page ad in Yellow Pages, probably $800.00/month)local outfit. On the other hand, they didn't install a ground rod, didn't upsize the GEC, and didn't extend it to <5' of water entrance.
I hope to eventually find out how much they charged.

[This message has been edited by Redsy (edited 09-02-2001).]

#78273 09/02/01 02:24 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Redsy,

If it's in the conduit it's not Direct Buried. If it's stripped is it still SE?
The conductors have to be rated for wet locations don't they? Anyone know an official position on this?

Bill


Bill