Using an offset nipple between a meter socket and an outdoor service disconnect would require a bonding bushing where some eccentric KO rings are left intact. The nipple is considered part of a service raceway. Correct?
|
|
|
|
Joined: Nov 2000
Posts: 2,236 Likes: 1
Member
|
I would tend to think so, at least, that's the way I interepret it...
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
|
Joined: Jan 2001
Posts: 75
Member
|
I interpret 250-80 requires this offset nipple to be bonded.
250-94(4) suggests bonding bushing or set-screw locknut.
Only one end of the metal "service" raceway needs to be so bonded.
If concentric KO's are encountered, bond both ends. Or at least the end that has any concentric KO's.
Glenn
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
I find it much less trouble to just use Pvc when possible. If a metal nipple was used here We would have to bond with a #6 solid Insulated (not taped) Green conductor. Try and buy that wire in a pinch. Bill
Bill
|
|
|
|
Joined: Nov 2000
Posts: 2,236 Likes: 1
Member
|
That, and my PoCo doesn't want any bonding bushing or #4 bare in their meterbase...
I use PVC too...
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
I don't believe that the bonding locknut is acceptable with concentric knockouts that have portions of the KO's remaining. It doesn't serve any more purpose than would a standard conduit locknut in this case.
|
|
|
|
Joined: Nov 2000
Posts: 246
Member
|
Bonding of this nipple (I assume it is not connected to a hub at one end, in the case of the meter socket above an outdoor rated panel) is required even if there is no concentric ko's. If it attached via a hub, no special bonding is required. If power companies don't want you in their sockets, and you need to bond it, either install a meyers hub on the panel, or install a grounding bushing inside your panel, or use a pvc nipple. Just make sure to bond the pvc with a nylon jumper!(ha-ha)
Rick Miell
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
It only needs to be bonded at one end, so there is no need to install something in the meter can that the utility doesn't want there. Don(resqcapt19)
Don(resqcapt19)
|
|
|
|
Joined: Jul 2001
Posts: 40
Member
|
I was unaware that there needed to be a bond to a nipple. I have connected service to thousands of customers and have never seen any sort of bonding at all to a nipple. The only thing I was ever taught to look for is the plastic bushings that protects the wire from rubbing the edge of the nipple. Even in the city (Houston) where they have inspectors and require permits I have not seen this practice.
Also what good would it do if it were only bonded on one side(breaker box). If the meter-can has knockouts then how would there be true continuity tying the two boxes together? Seems like a waste of time to only install a bond to one side. But as was stated by someone earlier, the utility does not allow "any grounds" in there meter can. As also we do not either.
Without the nipple having a true bond between the boxes has helped me to troubleshoot some neutral problems. If the neutral connection was ever lost in the breaker box then the load would try to use the nipple to conduct. If not bonded then it begins to spark/burn around the KO where the nipple makes contact with the box. It has gotten to a point now where I look for this tell tale sign whenever the cust mentions dim lights.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
glenn35, Maybe it's a local thing. Here, the PoCo even made the manufacturers add a separate lug to the Meter Pan to accomodate this bonding wire. I don't know for sure if they'd call for bonding in all situations though. When they stopped allowing the wire to be taped green I went for PVC and haven't looked back. Bill
Bill
|
|
|
Posts: 2,749
Joined: October 2000
|
|
|
|