1 members (Scott35), 413 guests, and 12 robots.
#78071 08/13/01 05:33 PM
tmon Offline OP
Does anyone know of a listed bonding fitting to connect conduit to a cable tray?
#78072 08/13/01 08:15 PM
I believe Crouse-Hinds has such a fitting. When I go in tomorrow, I'll get the model #.
#78073 08/13/01 08:38 PM
What we do is........
Install a bonding bushing on the end of the conduit. Jumper with #6 bare from the bonding bushing to a lug bolted to the rail of the tray. Fasten the conduit to the tray with a U-bolt clamp.
GJ
#78074 08/14/01 07:29 AM
Crouse-Hinds "LCC Series" Cable Tray Conduit Clamps. Page # 5F-19 of 2000 catalog.
#78075 08/15/01 06:07 PM
tmon Offline OP
Redsy,
Thank you that was the one I have been looking for. Tmon
