I would like to know everyones opinion on the grounding of every switch, receptacle and junction box. Are you guys requiring and/or installing a grounding jumper from the equipment grounds to the box?
#78065 08/13/01 06:55 PM
My opinion tmon, is not necessarily code driven as much as liability driven.
I say ground it ALL, a small price to pay for some sound sleep.
Of interest, i believe 380-12 addressed more stingent grounding of switches in the 99' code cycle.
#78066 08/13/01 07:51 PM
Could you be more specific?
As far as j-boxes, I dont believe you have a choice if an EGC is run.(See 250-148)
Receptacles, the only other option is self-grounding receptacles.
As far as switches, see 380-9(b)
#78067 08/13/01 09:17 PM
Ground it, Ground it, Ground it.
#78068 08/19/01 09:15 AM
250-148 (a) Says If you have a separate grounding conductor pulled in the box, it will be bonded to that box. Nuff said ?
#78069 08/19/01 09:20 AM
Shoot !!! another half answer, lemme do some more 'splainin' . Our specs at Dulles airport require that 1) You WILL pull an equipment grounding conductor, and 2) You WILL land it to any box it goes through - which, of course is very plain. Why ? you may ask.
In these days of cell phones, FRS radios, etc.. we find that RF has a nasty way of getting into and interfering with intricate systems. Also,Bill Summers stated several years ago that he wanted to see the practice of conduit bonding ended, then went into an expanation that convinced me thoroughly. There is the code, and a very quick reason.