Originally posted by SirJaxx:
You can legally load a #14 thhn conductor to 35 amps. In Table 310-16, If the conductor is operating in an ambient temperature between 70-77 degrees F. or 21-25 C. You can appy a correction factor of 1.4 to the 25 amps under the 90 degree column. Although the LoadCenter probably wouldn't be operating in this environment, and all conductors must be sized to highest temperature it will see, but the code does show that we can use this formula for derating. Am I wrong here?
The asterisk in T310-16 refers to 240-3 which limits OCPD to 15 amps for #14. The exceptions don't include general purpose branch circuit wiring, which I believe is the idea in this thread. When using #14, The 90 deg. column is only usable for derating purposes, but still won't allow higher ampacity due to 240-3(d).