0 members (),
35
guests, and
11
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Dec 2000
Posts: 84
OP
Member
|
A medical trailor is going to be transported to our Firefighters Training Academy. It will be used for testing for 4 days and then taken away. It will come equipped with a 60 amp. 120/240V. 60A. 4W. power cable and attachment cap. A 4W. receptacle will be installed near a subpanel to provide power. Is a ground rod required?
Frank (cinkerf)
|
|
|
|
Joined: Feb 2001
Posts: 62
Member
|
Does the medical trailer have a panelboard? If it does have a panelboard then I would consider it a structure. Which would lead to Article 250-32, etc., requiring a ground rod. If it doesn't, then I would consider the trailer as portable equipment. Which wouldn't require a ground rod.
[This message has been edited by Mike (edited 06-15-2001).]
|
|
|
|
Anonymous
Unregistered
|
The metal shell of the trailer must throughly and solidly bonded to the EGC. You should test the resistance and find it to be low (<2 ohms). If it isn't bonded properly, then I see the need to get it correctly bonded. I don't see the need for a ground rod. A ground rod doesn't make a dangerous trailer safer.
I'm also assuming that the trailer will have a steel jack that would provide a path to earth if lightning strikes the trailer. The trailer really should have metallic contact with the earth for lightning.
I'm assuming that the trailer has a panelboard - but I still consider it portable as evidenced by the fact that it will be rolled away after only 4 days.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
hmmmm; we need to become definitional here, is this a structure ?? is this a mobile home???is this a camper??
|
|
|
|
Joined: Dec 2000
Posts: 84
OP
Member
|
The Medical Trailor does have a panelboard.
Frank (cinkerf)
|
|
|
|
Anonymous
Unregistered
|
It's not a structure mainly because it is not erected on site. Yes, a camper could be a good comparison. But I suspect that no one cooks or sleeps in this trailer.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
to G-rod or not to G-rod , that is the Q. hmmm;
550-23(a), last sentence refers to 250-32, so does this mean only the disco gets the rod?
while we are on it, what about art 553 , floating buildings ???
|
|
|
|
Joined: May 2001
Posts: 176
Member
|
I would consider the trailer as portable equipment since it has a cord and attachment plug. Even though the trailer was probably manufactured to the stringent standards of MHMA and other required standards (which by the way are now a lot stricter than they were twenty and thirty years ago when I bought my first mobile home). The cord and plug have two phase conductors, a neutral and a ground. The receptacle supplying power to the unit is deemed as grounded and providing a ground return path. Having said all of that, I think I would insure the shell and frame are electrically connected to the ground in the cable. An ohmmeter check should suffice. If your meter is in the truck a couple of hundred feet away then a scrap piece of #10 connected to the frame and to the receptacle conduit should provide a suitable ground path for fault currents. A separate ground rod may set up a situation with circulating ground currents, and may cause additional problems.
|
|
|
|
Joined: Feb 2001
Posts: 62
Member
|
Read the thread "Carnival Tent" in IAEI BB. It doesn't matter what NEC article we "think" the medical trailer falls under. It's the AHJ's interpretation that counts
|
|
|
Posts: 32
Joined: June 2004
|
|
|
|
|