Electricians revenge
0 members (), 44 guests, and 8 robots.
#77278 05/19/01 08:27 AM
F
frodo Offline OP
given a 6" rigid conduit that contains 3 1550 mcm and a 4/0 ground, which has a STANDARD seal located immediately where the conduit stubs up out of concrete, then the conduit terminates at a large pull box.
i feel that this is a violation because the conduit is allowed 40% fill, but the seal is restricted to 25%.
#77279 05/19/01 09:32 AM
Tom Offline
I'm not going to do the math, I'll trust you.
You're correct that it is a violation to exceed the 25% fill unless the seal off is listed for more fill.
6" seal? Bet that was expensive.
Another thing I notice about seals is that a lot of guys like to use fiberglass insulation for the packing instead of the listed fiber made by the manufacturer of the fitting.
#77280 05/19/01 09:43 AM
F
frodo Offline OP
thank you tom,
i have 8 gas turbines with generators that have this problem. what do you suggest would be the fix if the cables are installed?
can the code be disregarded? i beleive the intent of the code here is to acheive a proper seal...
i say that one violatation is as serious as another and that the situation should be brought into compliance...
this is a dc circuit that will carry a substantial current...
i want it fixed but it will be expensive...
#77281 05/19/01 04:13 PM
Seals are usually upsized via EXP redcuers to meet the fill, but i have never heard of a 7" or 8" seal.
#77282 05/19/01 05:21 PM
What is the flammable fuel involved in this installation?
#77283 05/19/01 06:21 PM
F
frodo Offline OP
natural gas
class 1 div 2
gas turbines
#77284 05/19/01 07:09 PM
Is this a new installation or old work?
GJ
#77285 05/19/01 08:38 PM
F
frodo Offline OP
GJ
new installation at power house
#77286 05/19/01 09:05 PM
Then the contractor is responsible for the correction......unless it is in compliance with the engineering spec., in which case the engineer should pay.
GJ
#77287 05/19/01 09:19 PM
Tom Offline
What are you using as a basis for calling this a hazardous location? Is there some building code that is calling this a hazrdous location? Just because there is natural gas piping involved doesn't make this an explosion hazard, if it did, any house with a natural gas water heater would have hazardous locations.
I'm certainly not faulting your concerns about safety with the above questions, but I just can't see why sealing is required.