by NORCAL - 03/19/24 05:11 PM
0 members (), 260 guests, and 19 robots.
F
frodo Offline OP
can you install a 2" conduit in front of and to the left looking at the front of the panelboard (600VAC)?
as i read section 110-26 (2), (3) it appears that it would be a violation if the right edge of the conduit is lined up directly with the left side of the panelboard cover looking at it from the front. i have photos available as well.
the conduit is around 6" in front and to the left side of the panelboard....
Frodo,
If you project a line out from the left side of the panelboard the area must be clear for 36" minimum straight out from the front of the panel. If the line hits the 2" conduit then it's a no-no.....if the conduit is to the left of the projected line you're OK.
Hope that makes sense, if not ask again.
GJ
F
frodo Offline OP
Originally posted by golf junkie:
Frodo,
GJ
thanks,
i have a contractor that i am supervising and they have installed a 2" conduit so close to the rule it is questionable in my mind. as i read in 110-26 (3) i must consider (e) as well, in addition to the 6" maximum beyond the front of the equipment...
thank you for taking the time to reply...
regards
frodo
frodo;
i'm farily sure 110-26 (3) was made for troughs, but is ok for any pipework associated with the panel.
make sure your panel door can open 90 deg.----110-26-(2) with that pipe...