Originally posted by Don'tKnowEverythingYet:
I don't understand this at all. Where is the 8' measured from? How does this differ from 230-24b. Then 225-19a goes on to further confuse me by saying "vertical clearance in all directions" what other direction is there for vertical besides up and down?
Measure from the lowest point on the conductors to the roof surface directly below that point. That plumb line must be the center of a cylinder of the required height into which the conductors do not intrude.
If the roof slope is less than 4 in 12 or the voltage between the conductors exceed 300 volts the conductors must clear the roof by eight feet.
If the roof slope is 4 in 12 or greater and the voltage between conductors does not exceed 300 volts then the conductors must clear the roof by 3 feet when measured above the interior of the building or 18 inches when measured above the overhanging portion of the roof i.e. the soffit. If you use the eighteen inch exception the portion of the conductors length above the roof must be less than 6 feet long and must span a distance across the overhanging portion of the roof of four foot or less. Did I manage to make it any clearer.
225-19. Clearances from Buildings for Conductors of Not Over 600 Volts, Nominal.
(a) Above Roofs. Overhead spans of open conductors and open multiconductor cables shall have a vertical clearance of not less than 8 ft (2.44 m) above the roof surface. The vertical clearance above the roof level shall be maintained for a distance not less than 3 ft (914 mm) in all directions from the edge of the roof.
Exception No. 1: The area above a roof surface subject to pedestrian or vehicular traffic shall have a vertical clearance from the roof surface in accordance with the clearance requirements of Section 225-18.
Exception No. 2: Where the voltage between conductors does not exceed 300 and the roof has a slope of not less than 4 in. (102 mm) in 12 in. (305 mm), a reduction in clearance to 3 ft (914 mm) shall be permitted.
Exception No. 3: Where the voltage between conductors does not exceed 300, a reduction in clearance above only the overhanging portion of the roof to not less than 18 in. (457 mm) shall be permitted if (1) not more than 6 ft (1.83 m) of the conductors, 4 ft (1.22 m) horizontally, pass above the roof overhang, and (2) they are terminated at a through-the-roof raceway or approved support.
Exception No. 4: The requirement for maintaining the vertical clearance 3 ft (914 mm) from the edge of the roof shall not apply to the final conductor span where the conductors are attached to the side of a building.