ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 519 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline OP
Member
It seems that table 300-5, Column 5 requires low-voltage landscape lighting cables to be buried 6". Article 110-3(b) requires equipment to be installed per manufcturers instructions.
Hadco(high-end fixtures, accessories,etc.)catalog states that the low voltage cable does not need to be buried,just covered with mulch, stones, etc. It recommends 4" burial when crossing lawns to avoid landscape tool damage. I once contacted Malibu, and was again told that the low voltage cable is not required to be buried. I say bury it 6" everywhere. What am I missing?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2000
Posts: 2,148
R
Member
1) 110-3(b) does not tell you that you must follow the manufacture's instructions. It tells you that you must follow any instructions that are part of the listing and labeling.
2) There are listed "relocatable" low voltage fixtures and would not think that that cable would have to be buried in that the fixtures are intended to be moved around.
3) If the installation is to be "permanent" then I would require the 6" as shown in Table 300-5.
4) If the low voltage lighting system is not a listed system, then the cable requires 24" of cover.
Don(resqcapt19)


Don(resqcapt19)
Joined: Oct 2000
Posts: 5,392
S
Member
Don;
i've been looking at a lot of instructions since you have brought 110-3(b) to my attention.
(Thank You)