#76793 03/21/01 09:29 PM
Joined: Mar 2001
Posts: 4
T
Tim M Offline OP
Junior Member
I have spoke to supply houses who use the term URD for a direct burial type of cable similar to triplex. What is this found under in the NEC and UL Whitebook? Is it USE?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#76794 03/22/01 07:16 AM
Joined: Oct 2000
Posts: 5,392
S
Member
it comes marked USE/URD

[Linked Image]

#76795 03/22/01 04:41 PM
Joined: Nov 2000
Posts: 72
B
Member
Sparky must be in a hurry [Linked Image] This question appears often, and is asked quite frequently in the field. I have heard of inspectors not allowing cable assemblies identified as URD, for the reasons you state. The inability to locate any approval in publications, is the general reason.
URD, or underground residential distribution cable, can be USE, underground service entrance cable. When it is service entrance cable it is commonly, 3 conductors of Aluminum XHHW, with one conductor identified.
URD identified distribution cable can be medium voltage cable, in the range of 4.16 KV, to 34.5 KV. Of course this will not be marked as USE.

#76796 03/22/01 08:27 PM
Joined: Mar 2001
Posts: 4
T
Tim M Offline OP
Junior Member
Thanks. It helps to know what the abbreviations are. I then conclude URD/USE is used for primary and secondary for residential underground, and USE is secondary?

#76797 03/22/01 10:30 PM
Joined: Nov 2000
Posts: 72
B
Member
Tim: Only URD for 600 volts or less will be identified as USE.
URD for primary medium voltage will be PE, XLP, EPR, PVC, or CSP.