I have a small ups that I was going to have someone look at but haven't gotten around to it. I was at my brothers' company trying to figure out and label circuits for him and there was one We couldn't find for a good hour. We had a calcuator plugged into a receptacle and were watching it as We flipped the breakers. Nothing turned it off! The breaker He told me it was did not turn off the calculator. After insisting that it was the right one We shut it off and I pulled the breaker out of the panel. The calculator was still on & I tested the wire on the breaker and got 115 volts! A ups that was plugged into an outlet on that circuit was backfeeding the circuit through it's plug!
So, you never know what you might find! Anybody got an Idea how that could happen?
Bill
Bill
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Sparky, Your original post stated: All other circuits in the 120/208V 3 phase panel showed normal fluctuations in voltage and current. The voltage was steady on the questionable circuit on the line side of the breaker, but fluctuated as described above at the receptacles.
This appears to m to be nothing more serios than some type of poor connection somewhere between the panel and the loads. Don(resqcapt19)
Don(resqcapt19)
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Bill, the incident i mentioned was a stinky little UPS, cept' it was introducing a pulse on the circuit... probably built by the same satanic order 66'....what did you weed out there pal? We're all on the edge of our keyboards here...
|
|
|
|
Joined: Nov 2000
Posts: 2,236 Likes: 1
Member
|
Fluorescent lights under the counter on the opposite side of the 'puters. They were sharing the circuit. I'm not certain they were causing the flucuations, but they couldn't help. The circuit was also being shared with the office next door and was difficult to troubleshoot.
The dedicated circuit must have solved the crashing problems cause they've paid their bill!
[This message has been edited by sparky66wv (edited 02-24-2001).]
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
|
Joined: Feb 2001
Posts: 54
Member
|
Your place in question is next door to a doctors office? and they share a power panel? Dunno about ya'll, but my doc has his own X-ray machine, among other diagnostic items..... One place I worked, Someone had placed a sign on one of the welders, 2 rooms away from the Maint supply guys desk, stateing, that if you needed to weld, you needed to inform him to shut down his computer. It was dated 10 years before i started working there. Well we started X-perimenting, and found out that they were both fed from the same panel, we also found out that the physical location didn't matter much, end result we re-wired the comps recept's to a panel on another X-Former solved the problem.....
|
|
|
|
Joined: Nov 2000
Posts: 2,236 Likes: 1
Member
|
Said business is rebuilding and moving soon, so I didn't complain much about the setup.
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
|
|
|
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
|
|
|
|
|