cinkerf Offline OP
What determines if a building requires a fire alarm system.
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#76075 12/03/00 11:04 AM
See the 1999 NEC, Section 700-1, FPN No. 3:
Emergency systems are generally installed in places of assembly where artificial illumination is required for safe exiting and for panic control in buildings subject to occupancy by large numbers of persons, such as hotels, theaters, sports arenas, health care facilities, and similar institutions.
Emergency systems may also provide power for such functions as ventilation where essential to maintain life, "fire detection and alarm systems," elevators, fire pumps, public safety communications systems, industrial processes where current interruption would produce serious life safety or health hazards, and similar functions.
#76076 12/03/00 12:19 PM
The requirement for the installation of a fire alarm systm is found in the life safety and other building codes. The installation of any fire alarm system, required or not, is covered by NFPA 70(NEC) and NFPA 72 (National Fire Alarm Code).
Don(resqcapt19)