JBD, it did say something about it being series rated.. or something, never seen that before on a panel, what do they mean by that?
aldav,
I'd suggest using the 'search' feature of this site to look up the following terms: 'series rating', 'available short circuit current', 'SSCR'. You will find lots to read up on.
In a nut shell, when you have a short circuit, the current flow is limited by the characteristics of the supply transformer, the circuit up to the point of the fault, and possibly any motors connected to the system that could regenerate power into the fault. The circuit breaker itself does _not_ limit the current flow significantly. It is the job of the circuit breaker to _interrupt_ this current flow. Available fault current is generally much greater than the continuous rating of the loads served; in residential applications with 100A services, fault current requirements of 2500A to 10000A are quite common.
If the short circuit current flow is too high, then the circuit breaker will _fail_. The current that a breaker is capable of interrupting is one of the ratings of the breaker, just like voltage or trip current. The breaker must be rated to interrupt the available fault current.
A 'series rating' is an exception to this general rule. Generally you have multiple breakers in series, eg. the main breaker at the service, followed by a breaker supplying a feeder to a panel, followed by a branch circuit breaker in the subpanel. The 'series rating' permits you to use specific combinations of upstream and downstream breakers, where only the upstream breaker is rated for the available fault current. To use a 'series rating' you are limited to using those _specific_ breaker combinations that have been tested. You need to evaluate the feeder as well as the panel that you are looking at to select a suitable branch circuit breaker.
-Jon