0 members (), 376 guests, and 7 robots.
#74705 02/02/07 11:34 AM
Rob Offline OP
How do you determine operating cost of a 3 phase motor. 460 volt 15 amp.
My utility rate is .08 cents per kwh.
Is there a common formula?
#74706 02/02/07 11:58 AM
Measure the actual amps drawn on each leg. Average. Multiply by 1.73. That's your amp load.
From there, it's the usual amps x volts x time x rate = electrical cost.
This will give you figures good enough to work with. Actual results will vary a bit, due to changes in load, power factor, harmonics, etc ... but the number you get will be close enough for budgeting.
#74707 02/02/07 06:20 PM
JBD Offline
One quick and dirty method is to estimate 1KVA of input power for each HP of output.
For a fully loaded motor you can use 1KW per HP. For lightly loaded motors use 1.1KW per HP instead.
