by HotLine1 - 04/23/24 02:17 PM
0 members (), 231 guests, and 11 robots.
#73783 01/02/07 10:02 PM
ElJay Offline OP
Is it legal to come off the bottom of an existing meter socket to a sub-panel other than the main breaker panel as long as wire is sized correctly and over-current protection is sized properly.
#73784 01/02/07 10:17 PM
The lugs in the Meter would have to be listed for mutiple conductors, the panel would have to be located in close proximity to the existing panel and have a main or no more than 6 breakers combined in the panels (with an exception for TVSS) see 230.70 thru 230.73.
It would not be treated as a "Sub-Panel" but as a Main panel
Roger
[This message has been edited by Roger (edited 01-02-2007).]
#73785 01/02/07 10:19 PM
Yes, you can if it is rated for a double tap.But it wouldn't be a sub panel, you would have another main breaker panel.
#73786 01/02/07 10:22 PM
Beameup, I think I was editing as you were posting.
Roger
#73787 01/05/07 12:53 AM
Yup, I think so. Oh well we both said the same thing [Linked Image]