1 members (Scott35), 528 guests, and 22 robots.
#72994 12/14/06 09:39 PM
bdonus Offline OP
need to know what size groung conductor to use for the main ground to the water pipe for a 1600 amp service with 4 sets of 600 mcm cables to the utility transformer.
#72995 12/14/06 10:24 PM
With the information given, table 250.122 shows 4/0 if the egc is copper, or 350 if it's al/cu. 250.122 (F) talks about conductors in parallel also. This should get you started.
Luke Clarke
Electrical Planner for TVA.
#72996 12/14/06 11:58 PM
You use 250.66, not 250.122
I read it as the max required will be 3/0 copper or 250 MCM al.
#72997 12/15/06 12:23 AM
Thanks, and apologies for the mix-up, 250.122 is for grounding raceway's and equipment. Seen that first part, where it says minimum size egc, and the rest is history. [Linked Image]
Luke Clarke
#72998 12/16/06 10:10 PM
Y
If under the Chicago code its 18-27-250.66 page 93
copper (300) in a 1 1/4 inch conduit or tubing.
