0 members (), 373 guests, and 12 robots.
#72931 12/11/06 09:58 PM
Coming from the breaker I have 240 but it drops down to 167 when I try to start blower motor. This goes through a phase converter. What could be the problem. I tested from the breaker
#72932 12/12/06 12:36 AM
How far away is the motor from the supply source?
What type and size are the conductors?
Phase converter's.... never worked with them before.
#72933 12/12/06 01:47 AM
Don't know about this in the "real world" but I remember reading that there needs to be a transformer to adjust the supply voltage before entering the converter, to ensure the correct three-phase voltage (208?)...
is the 167V at the breaker? Have you tested if the three-phase is balancing properly?
hmmm.... *confused*
#72934 12/12/06 03:14 AM
it is 50 feet away using #10 wire . it is a soil vapor extractor first time at this site. it is along the railroad and the power is coming from a drop from the railroad pole.
#72935 12/12/06 08:58 AM
What is the blower load?
With the blower off what is the voltage after the phase converter?
Earl
#72936 12/12/06 09:19 AM
#72937 12/12/06 09:25 AM
Z
If the supply voltage drops at the breaker, I would guess first that the problem is with the supply, and that the extra load is bringing the problem to the surface. It's probably either the PoCos problem, or you have a bad connection on your side.
Try tightening all lugs on your mains coming into the panel, and everywhere else that you can get to. Make sure all the busses are in good condition and that your breakers are seated properly and the contacts are all in good condition.
If that does nothing, call in your PoCo to check their connections at the x-fer and behind the meter (if you can't get behind the meter yourself because they have it locked out). ALWAYS BE THERE WHEN THEY COME OUT so you can show them the problem UNDER LOAD, or they will not see the problem at all.
I see this problem a lot pretty often,and it's usually a loose connection or a bad main feeder.
Please let us know what you find, and good luck!
#72938 12/12/06 09:41 AM
IT IS ON THE RAILROAD .. WE ARE GOING TO BRING IN GENERATOR IF WE CAN'T FIND A PROBLEM. I AM JUST WONDERING IF I HAD A BAD STARTER WOULD THIS CAUSE THIS.. I AM NOT ELECTRICIAN BUT HAVE GENERAL KNOWLEDGE. WHAT ABOUT THE PHASE CONVERTER ITSELF ? THANKS FOR YOU HELP
