I have a 200A panal in my house and would like to put a 200A sub in my barn. I know seimans dont make a 200A 2pole breaker. Is there a lug kit i can put in this panal to feed the sub? Any other options?
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Harlie, contact a local Electrician, they will be able to help you.
Roger
|
|
|
|
Joined: Nov 2001
Posts: 273
Member
|
harlie, why not put a seperate meter on the barn? copper is pretty expensive for a 200 amp feed,unless it's real short. but as roger said please contact an electrician
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
What kinds of loads will there be in the barn?
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
I can't think of a reason that you would want to put in a 200A subpanel fed from a 200A panel. If your load in the barn is that great, chances are you would need to upgrade the service at the house. I don't know if it's an alternative, but will the PoCo give you a separate service at the barn?
|
|
|
|
Joined: Jul 2004
Posts: 625
Member
|
I'm guessing that Harlie has, or has his eye on, a "200A panel", and figures that he needs to supply it with a 200A supply.
Harlie, that's not necessary. Your supply needs to be sized according to the load calcs in the Code, which will almost certainly be less than 200A. It is very likely you can feed your 200A panel with a 50-100A feeder.
[This message has been edited by SolarPowered (edited 12-13-2006).]
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Sep 2006
Posts: 111
Member
|
All panels have a "per stabb" rating on the inside of the cover. A 200a panel usually has a max of about 70a per stabb. You can't run a 200a circuit from a 200a pqnel. Check the "per stabb" rating on the panel.
|
|
|
|
Joined: Oct 2001
Posts: 172
Member
|
Eddy Wouldn't that make the 80 - 125 amp plug on breakers useless?
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Eddy I have never seen a per stab ratting as low as 70.
I have seen 100 per stab but that does not prevent larger breakers.
A 2 pole 150 amp breaker for a 200 amp panel will use two stabs per phase.