1 members (Scott35), 216 guests, and 10 robots.
#72843 12/11/06 07:03 PM
I have a 200A panal in my house and would like to put a 200A sub in my barn. I know seimans dont make a 200A 2pole breaker. Is there a lug kit i can put in this panal to feed the sub? Any other options?
#72844 12/11/06 07:30 PM
Harlie, contact a local Electrician, they will be able to help you.
Roger
#72845 12/12/06 08:42 PM
harlie, why not put a seperate meter on the barn? copper is pretty expensive for a 200 amp feed,unless it's real short. but as roger said please contact an electrician
#72846 12/12/06 11:00 PM
What kinds of loads will there be in the barn?
#72847 12/12/06 11:26 PM
I can't think of a reason that you would want to put in a 200A subpanel fed from a 200A panel.
If your load in the barn is that great, chances are you would need to upgrade the service at the house.
I don't know if it's an alternative, but will the PoCo give you a separate service at the barn?
#72848 12/13/06 01:05 AM
I'm guessing that Harlie has, or has his eye on, a "200A panel", and figures that he needs to supply it with a 200A supply.
Harlie, that's not necessary. Your supply needs to be sized according to the load calcs in the Code, which will almost certainly be less than 200A. It is very likely you can feed your 200A panel with a 50-100A feeder.
[This message has been edited by SolarPowered (edited 12-13-2006).]
#72849 12/13/06 03:32 AM
e57 Offline
"seimans dont make a 200A 2pole breaker."
They don't?!? http://www.sea.siemens.com/resident/images/Circuit%20Breaker/Q2200B.jpg
http://www.sea.siemens.com/resident/images/Circuit%20Breaker/MBK200A.jpg
http://www.sea.siemens.com/resident/images/Circuit%20Breaker/QN2200.jpg
http://www.sea.siemens.com/resident/images/Circuit%20Breaker/QN2200R.jpg
Edit due to pic's being so big you could see the finger-prints of the photographer.....
[This message has been edited by e57 (edited 12-13-2006).]
#72850 12/13/06 07:47 AM
All panels have a "per stabb" rating on the inside of the cover. A 200a panel usually has a max of about 70a per stabb. You can't run a 200a circuit from a 200a pqnel. Check the "per stabb" rating on the panel.
#72851 12/13/06 08:43 AM
Eddy
Wouldn't that make the 80 - 125 amp plug on breakers useless?
#72852 12/13/06 08:52 AM
Eddy I have never seen a per stab ratting as low as 70.
I have seen 100 per stab but that does not prevent larger breakers.
A 2 pole 150 amp breaker for a 200 amp panel will use two stabs per phase.