An existing, buried, empty, 2-inch GRS conduit is to be used for a new application. One end stub-up remains as is, the other end will be relocated. The idea is to remove a portion of the conduit and replace it with a new portion that is routed to the new location.
What type of conduit connection would you recommend?
Could the existing conduit be threaded in place in the trench?
What method could be used to cut and thread it without removing it from the trench?
Rich
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
You can hand thread 2" with a 2" NPT die, handle and oil supply. Better than a manual handle would be a portable power threader. This tool combined with a 2" die and you will be done in under a minute. Model 700 Power Drive Just hang on tight...... [This message has been edited by iwire (edited 11-22-2006).]
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Feb 2005
Posts: 361
Member
|
Stick a 5' piece of 3/4 in the handle (the handle is threaded)...much easier to hold...but you may need someone to hold the button down.
~~ CELTIC ~~ ...-= NJ =-...
|
|
|
|
Joined: Dec 2004
Posts: 1,064
Member
|
Don't they make a rigid compression coupling that is listed direct burial?
|
|
|
|
Joined: Jan 2005
Posts: 109
Member
|
A word of warning. I have had the threads on the next coupling back strip and break threading in place. If possable I would look for a joint to cut. Otherwise I would have a helper hold the pipe from spinning. Rod
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
If you cant get/rent a threader like that, shoot for the ole' skool method and get a regular racheting die, and put your back into it.... (Or someone elses back) 3 forward - 2 back after you get it started, and use plenty of fluid.
Or if using a compression fitting - go for stainless tape tight with 20 mil, and if you really feel like you're cheating and your not.... Pour a little form of concrete. As for getting it tight enough - a trick I learned right here at ECN from Electure is to use a hammer drill with a chisle bit to work the edges of the fitting into getting tighter than possible with a wrench.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Jul 2002
Posts: 680
Member
|
iwire has the ticket, I thread pipe in the ground all the time with 700. 3 piece coupling and you're good to go. I wouldn't trust 3/4 pipe to hold a 700 back though, if the pipe breaks and it will on the thread the 700 might rip you a new one. If I couldn't hold it, I'd slip a piece of 2" over the handle. Definitely hold the pipe you are threading with a wrench so as not to spin it. Livetoride is correct, you can break it at the next coupling.
|
|
|
|