ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 555 guests, and 34 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Jan 2003
Posts: 4,391
I
Moderator
Bob I am nit sure what you mean by

"New service complete includes 2 new ground rods that I installed to code."

I work in many new buildings that do not have any ground rods, they are not always required.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Sep 2005
Posts: 120
Z
Zog Offline
Member
OK, lets clear up some things about ground rod testing. To test you drive 2 test rods in the ground. The 1st one is called "Z" and is refered to and the current rod, should be placed about 100ft or so from the rod under test. The 2nd rod is called "Y" and is refered to as the potential rod should be placed 62% of the distance of "Z".

The test set creates a circuit from the rod under test through "Z", through earth, and back to the test set. The voltage at "Y" is measured and used to determine the resistance to earth of the rod under test.

Now, the rod under test and "Z" will have a sphere of influence that may cause your voltage reading at "Y" to be inaccurate. So a "Y" gets moved to 52% of Z and 72% of Z and the results are plotted. If the readings of the 3 tests are similar you know you have a good test, if there is a difference then the spheres of influence are affecting your readings and "Z" must be moved further from the rod under test.


MV/HV Testing Specialist, "BKRMAN"