#7190 01/25/02 10:02 AM
buddy Offline OP
This is probably a simple question for this group. A co-worker recently had a residence rewired and has experienced the light bulbs in one hallway burning out every couple of weeks. Any thoughts on what is causing this?
#7191 01/25/02 11:59 AM
Loose neutral (in home run, splice, etc.) poorly made edison base sockets for the bulbs, poorly made, maybe imported light bulbs.
#7192 01/25/02 02:56 PM
Bulbs could be loose or subject to vibration somehow from the floor above, slamming doors, etc. Try a rough service bulb in the fixture.
#7193 01/25/02 11:57 PM
As the others said. Most likely a loose neutral somewhere, obviously try looking at the fixture first. Last resort, try a 130v incandescent lamp. Covers many a problem.
Cheers
NS4M
#7194 01/26/02 11:13 AM
NS4M has the right idea. There is a formula for incandescent bulbs in our apprenticeship books that says:
(Actual Life/Rated Life) = (Rated Volts/Actual Volts)^13.
Take a 130 volt, 1000hr rated bulb and feed it 123 volts and you get:
AL/1000=(130/123)^13 or 2053 hours actual life.
In contrast, take a 120 volt 1000hr bulb and feed it 123 volts and you get:
AL/1000=(120/123)^13 or 725 hours actual life.
Those 130v bulbs are life savers in hard to reach fixtures.
