New install in a retail store. Adjacent receptacles in a telcom room on a 12/3 MC homerun. If nothing is plugged in, you have 120 V to neutral on each circuit. If you plug in a security system transformer you have 200+ volts to neutral on the other circuit(which still has nothing plugged into it). If I unplug that and plug my 3 prong tester into the circuit I Read 176 volts to neutral on the other circuit. The condition came to light when the inspector plugged his 3 prong tester in to the second circuit with the transformer plugged into the first and saw two green lights and an orange. What am I missing here? Checked the wiring and found no problem---ckts are on different phases and share a neutral. 120 volts is derived from a transformer since this is a 480/277 service.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
It really appears the neutral is not correctly wired.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Nov 2005
Posts: 827 Likes: 1
Member
|
I sure hope that your Neutral is coming from the bonded secondary center tap of that transformer. Joe
|
|
|
|
Joined: Oct 2002
Posts: 482
Member
|
I've seen very similar readings from loose or mis-wired neutrals also. That would be my first guess. Please let us know what you find out...
|
|
|
|
Joined: Jun 2005
Posts: 124
OP
Member
|
Went back and looked in the panel today. The guy who made it up had the neutral from the 12/3 spliced to a piece of white THHN because it would not quite reach the neutral strip on the bottom of the panel. I followed this THHN down, across the bottom of the panel, past the neutral strip, back up the other side of the panel where it was wirenutted to the neutral tail from a GFCI breaker. Apparantly he had intended to use this piece of THHN to lengthen both neutrals so they would reach the strip. All he forgot was to CUT IT IN THE MIDDLE AND ATTACH EACH ONE TO THE NEUTRAL STRIP!!! Keep your eye on your help and never assume anything.
[This message has been edited by poorboy (edited 10-24-2006).]
|
|
|
|
Joined: Mar 2005
Posts: 1,213
Member
|
LOL!!!! I shouldn't laugh, though, sounds like something I'd do!
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
It's amazing how much better something works if it's wired up correctly!
|
|
|
|
Joined: Oct 2002
Posts: 482
Member
|
Thanks for the update poorboy. I'll keep that information in my troubleshooting brain-file...
|
|
|