763
20
Id tell the home owners what the inspector said and then tell them I have no way of "proving" what the panel is so you'll need a new panel. Let them deal with the inspector, I bet he'll change his tune.
Sounds good but the house is vacant and under foreclosure as best I can tell.
Byron
Is there a jumper missing between the left and right Neutral/Ground bars? (3rd photo)
Is the panel even rated 3R?
Is the 100A CB rated as a "Main" (where's the screw)?
I would advise whomever called you out there, that the panel is not of any known variety ...and can't be "proved" ...I would recommend changing it out.
~~ CELTIC ~~ ...-= NJ =-...
The reason so many mfgs make that type of breakers is to have their product fit the maximum number of panels. How can an inspector require proof? either they fit or they don't. Generic panels accept any breaker that will fit. It could be ite/siemens, milbank, midwest, CH, murray. The style of neutral liiks siemens or challenger to me. Perhaps inside the meter socket will be a mfg id...Ask your inspector what constitutes proof and ask who his boss is. Sounds like the peckerwood has a tiny bit of power and wants to have you do some kinda dance for him.
Thanks for the comments!
Celtic, since when are all residential panels required to have screws on the main? I know all the new panels I've installed are that way but Zinsco, old GE and others do not have that screw.
Thanks!
Looks like a perfectly acceptable older model Siemans / ITE "All In One" load center.
It IS rated Nema 3R.
The 100 amp breaker is listed as the service disconnecting means.
The UL web site has a list of interchangeable breakers. Offhand, I don't see any problems.
It does appear tjat there are suitable sized wires from the meter pan to each ground / neutral bar.
There ought to be a 'dead front' cover for it, though.
Posts: 943 Likes: 2
Its a 1960s vintage ITE panel, pre CTL type panel (bus stabs are not notched).
Please note, Requirement for a hold down on a back fed main did not show up until the 1990 NEC 384-16 (f).
Added note.
[This message has been edited by NORCAL (edited 10-17-2006).]
The giveaway is the hook where the breakers hook under, on the wire terminal end of the breakers. That looks like Seimans to me too. (hate that style hook).