Ok So the light fixture on my Saltwater fishtank is leaking current. When I touch the fixture I can feel it and I can really feel it with 1 hand in the water. Any ideas on how to fix this problem? They sell these ground probes which I am going to get but thats taking the current from the tank.... http://www.marinedepot.com/aquarium_miscellaneous_titanium_grounding_probe.asp?CartId= maybe I should bond the fixture? I'm sure that was done at the factory but I dont know why im getting shocked. [This message has been edited by Trick440 (edited 10-02-2006).]
Shake n Bake
|
|
|
|
Joined: Dec 2005
Posts: 869 Likes: 4
Member
|
Do an insulation test on it which will give you the condition of the insulation of the wiring and the fixture. Possible a poor termination or loose strands may touch the outer exposed metal. Bear in mind that you have a dangerous situation at the moment and do not touch it with your hand whatsoever. Chance of electrocution is possible. Take it out and test it or get a new one, at the moment it is dangerous !!
The product of rotation, excitation and flux produces electricty.
|
|
|
|
Joined: Aug 2005
Posts: 251
OP
Member
|
Its very common to feel some shocks in saltwater. Its 'Salt' water, very conductive. So I'm not worried about the shocks to much. I just want to find a cure the common problem.
But I would do an insulation test if I knew what that was. I'm hoping to cure this with an easy bond... or is that to simple.
Shake n Bake
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
Play the odds...
The odds are that you are dealing with capacitive coupling to the salt water.
Your ONLY solution is to drain this EMF potential to ground.
The exact same effect can be had in hot tubs with ungrounded ( pre 1962 ) wiring. Any hot tub will build up quite a potential....
But the amps should be low....
Bleed them off through a sweet ground.
The zap will be gone.
Tesla
|
|
|
|
Joined: Oct 2004
Posts: 132
Member
|
I've worked on a few saltwater aquariums and have not been shocked. I have done work for a "fish tank cleaning guy" that probably works on 30-50 different salt aquariums a week, and I know none of them shock him.
I don't think it's safe to say that it's common to recieve a shock in saltwater. You have a problem with your equipment, find the problem and get rid of it or the equipment. Also, you should put all your saltwater equipment on GFI's. I have found faulty pumps tend to trip them out, especially the cheap pumps from overseas. Check heaters as well.
|
|
|
|
Joined: Nov 2005
Posts: 827 Likes: 1
Member
|
You might consider getting rid of the Electric Eels too. Joe
|
|
|
|
Joined: Mar 2004
Posts: 814
Member
|
Har Har that was a good one Joe.
|
|
|
|
Joined: Jan 2006
Posts: 558
Member
|
Perhaps completely isolate it with an isolation transformer???? A.D
|
|
|
|
Joined: Mar 2005
Posts: 1,803
Member
|
Wood work but can't!
|
|
|
|
Joined: Aug 2005
Posts: 251
OP
Member
|
capacitive coupling ... I like that.
I'm gonna try the ground probe I posted and then I'm going to bond the fiture to a definate ground.
And Mhulbert... you might wanna ask your fish guy, cause theres current in saltwater fish tanks all the time. With saltwater, it damn near travels through the air.... especially when you have so many watts being pulled by these fixtures.
My setup is not very large and its 2 x 250w MH at 480v (it think it was 480) after the transformer, and then 2 more transformers powering 4- 80w t5 light.. with fans, moonlights, etc, and thats just 1 fixture.
And you also don't GFCI your pumps. A tripped GFCI could easily mean a $2500 loss in corals and fish.. and thats just a moderate setups loss.. a large setup the loss would be even greater.
Shake n Bake
|
|
|