#69672 09/16/06 08:24 AM
Joined: Mar 2002
Posts: 125
S
Member
Having a bad morning,what is the wire size for 50 amp generator. Told the H.O 6-3. Doesn't want to pay. He already has 8-3 ran from previous install of portable. Thanks

#69673 09/16/06 08:49 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
If it is 8/3 NM than it is rated 40 amps because of 334.80

If was 8/3 MC or 8 AWG in conduit it would be rated 50 amps.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#69674 09/16/06 09:13 AM
Joined: Mar 2002
Posts: 125
S
Member
It is 8-3 NM thats why I told him that.

#69675 09/16/06 01:10 PM
Joined: Oct 2005
Posts: 100
J
JJM Offline
Member
Even #6 AWG is STILL inadequate.

Conductors for standby generators need to be sized not less than 115% of the generators nameplate rating: NEC 445.13. In this case 50A x 115% = 57.5A, so you need to go with #4 AWG minimum in this application.

Joe

#69676 09/16/06 01:22 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Joe that is a good point.

However I believe Sparks gave us the breaker size which is not the same as the generators rating.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#69677 09/16/06 03:35 PM
Joined: Mar 2002
Posts: 125
S
Member
I forgot about the 115% rule. The genorator is rated at 50 amps. It's been awhile since iv'e installed one. It is going to be one of those Bryant all-in-one setup. The only proble is that where he wants it is about 40' away. And he wants to try to reuse what he has. Thanks again Sam

[This message has been edited by Sparks30 (edited 09-16-2006).]