|
0 members (),
228
guests, and
10
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Mar 2005
Posts: 1,213
OP
Member
|
Are those cheap 15A receptacles rated to be wired up as a pass-through for a 20A receptacle circuit? EG, put the wire in from panel on one screw, and out to the next rcpt on the other screw? There isn't any labeling on them to indicate that the jumper bar is rated for 20A, but I've seen this done before.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Yes, and you can find the info in the UL white book (General Directory)
If you really look at the same grade and brand 15 and 20 amp receptacles you will find the 'guts' are the same only the plastic face is different.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Steve, I agree with Bob, and will add that if you are dealing with a multi-wire branch circuit the neutral must be pigtailed, see 300.13(B)
Roger
|
|
|
|
Joined: Mar 2005
Posts: 1,213
OP
Member
|
Thanks guys, that makes it easy I only have 1 multiwire string in the whole house (two 240V 30A tool outlets in the shop) and was planning to pigtail it regardless!
|
|
|
|
Joined: Oct 2005
Posts: 39
Member
|
we always pigtail both hot and neut."pretend there is only one screw on each side"
Patrick
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Steve if your 240 volt tool circuit doesn't have a neutral, it's not a multiwire branch circuit.
|
|
|
Posts: 32
Joined: June 2004
|
|
|
|
|