ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 260 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#68022 07/27/06 05:22 PM
Joined: Aug 2005
Posts: 251
T
Member
Whats the formula to find the amps a neutral is carrying?

And if 220 doesn't need a nuetral to work,.. is there current on the nuetral?

So I need some schooling an nuetrals. Any and all help is appreciated. [Linked Image]


Shake n Bake
Joined: May 2002
Posts: 1,716
R
Member
Trick,
Quote
Whats the formula to find the amps a neutral is carrying?
are you asking about three phase or single phase?

Quote
And if 220 doesn't need a neutral to work,.. is there current on the nuetral?
Since a neutral is not needed in this voltage (not true of all world voltage systems)source, it doesn't exist to have current flowing on it.

Roger

Joined: Aug 2005
Posts: 251
T
Member
Single phase.

Three phase wouldn't hurt either.


Shake n Bake
Joined: Dec 2004
Posts: 1,064
D
Member
For a wye system the nuetral current is calculated by:

N= Sq root of (A^+B^+C^)-(AB+AC+CB)

^=squared

For split phase(single phase) the nuetral current is calculated by:

A-B or B-A.

Does this make sense?

Joined: Aug 2005
Posts: 251
T
Member
nope it don't make sense.

The Wye formula I see and understand.. except for, What is A, and B?

The single phase. Same situation, what is the A and B refering to. Volts, Watts, amps?

And with this slash (-) are you tring to say A, minus B?


Shake n Bake
Joined: Dec 2004
Posts: 1,064
D
Member
Trick, the A,B,C are the currents in phase A, Phase B, and Phase C.

So for a split(single)phase service, the nuetral current is the unbalnced current flowing between phase A and phase B.

So if 30 amps were flowing on phase A, and 15 amps were flowing on Phase B, the nuetral current would be: Yes it is a minus...

A-B=N
30-15=15

On a wye service, if we had 150amps on A, 110amps on B, and 75amps on C.

N= Sq root of (A^+B^+C^)-(AB+AC+CB)
N=Sq root of (150^+110^+75^)-((150*110)+(150*75)+(75*110)
N=Sq root of
(22500+12100+5625)-((16500)+(11250)+(8250))
N=Sq root of
(40225)-(36000)
N=Sq root of
(4225)
N=65 amps


How does that look?



[This message has been edited by Dnkldorf (edited 07-28-2006).]

Joined: May 2002
Posts: 1,716
R
Member
Trick, to go along with Dnk's posts here are some graphics for help in visualizing the single phase neutral

BTW, I like to refer to the ends of single phase windings as legs, not phases.

So with this said, A and B in Dnk's post would relate to legs 1 and 2

[Linked Image]

[Linked Image]

[Linked Image]

Roger

[This message has been edited by Roger (edited 07-28-2006).]

Joined: Aug 2005
Posts: 251
T
Member
Thats great guys. I see now. Thank you. [Linked Image]


Shake n Bake
Joined: Dec 2004
Posts: 1,064
D
Member
Anytime.......

Joined: Nov 2002
Posts: 794
Likes: 3
W
Member
All the above assumes that all loads are pure resistors, like incandescent light bulbs. If we talk about a computer server farm fed by 3 phase 120V, things get more complicated. Computer power supplies draw large spikes of current at the very peak of voltage of the phase they are connected to. When the voltage on phase A peaks, computers on phase A draw their spikes of current and return them to the neutral. Later, 120 degrees of the 60Hz cycle, phase B peaks, and computers on phase B draw their current spikes, and return them to the neutral. Likewise, 120 degrees later for phase C. No overlap of these current spikes (in terms of time). Spikes last about 5% of the cycle time. Note that the neutral will see 3 times as much spike current than any one phase (assuming equal phase loading). Thus you'd need a thicker wire for the neutral.

[This message has been edited by wa2ise (edited 07-30-2006).]