1 members (Scott35), 381 guests, and 13 robots.
#67572 07/10/06 11:21 AM
bman Offline OP
Have installed a back fed 120V/208Vy-480V delta Xfmr to supply a 480V steam generator (ungrounded). 250.21(4) states I must install ground detectors on this system. Any one know of a source for gound detectors? I am thinking there must be a set up something like a panel surge arrestor
that I can attach at each end of the system?
Haven't been able to google anything up.
Thnx Bman
#67573 07/10/06 07:28 PM
Go To Erickson by clicking here
Then to the "ground detectors" button on the left
#67574 07/10/06 09:36 PM
The cheap and simple way is with 25 watt 250 volt lamps.
Take 6 lamps and pair them up in groups of 2.
Series each group then attach one group to each phase . On the other side of the groups
tie those wires together and take them to a normally closed pushbutton. That will act as a lamp test switch ,the other side of the switch connect to ground .
When every thing is normal all 6 lights will glow dim .When there is a ground the grounded phase lamps will go out or very dim and the other lamps will get bright. It is not hitech but it works very well.
