Scott35, thanks for all of your explanations.
Thank you for the kind words, and for checking out the stuff posted here!
Glad to be of help!!!
Amperes
Interrupting
Capacity.
AIC is typically rated in "kilo-Amperes", or "X * 1000" Amperes (10 KAIC = 10,000 AIC).
There is another abbreviated term:
A.I.R.This is Amperes Interrupting Rating
"A.I.R." (Interrupting Rating)is actually the marked rating on the Circuit Breaker, as established by testing.
"A.I.R." is also more related to the Bus Short Circuit rating and bracing than the term "A.I.C."
"A.I.C." (Interrupting Capacity) is the _Actual Test Current_ + Laws, which the Circuit Breaker "sees" during testing, for standard circuit breaker applications (as paraphrased by IEEE!).
Something to consider when figuring SCA at various points along a system:
Motors, along with Reactive Loads (like Ballasts, Discharge Lighting, Inductive Heating, Arc Welders, etc.), are major contributors of Fault Current.
These items need to be figured into the available Fault Level from the Power Transformer, for a complete SCA value.
The Reactive contributions on projects having less than 10 KVA of Reactive type Loads (Motors + XL / XC devices), are normally not significant enough to impact things - mainly because the Power Transformer may only be able to supply 4KA fault current, and all the Reactive loads combined would only contribute another 1KA maximum fault current - if even that much!
For instance, this example customer might be fed from a 208Y/120V 3 Phase 4 Wire pole mounted Transformer array, with a capacity of 50 KVA - and an "overall" Impedance of 1.6% Z.
The available SCA at the Transformer(s) is somewhere around 9KA.
Let's say the customer has an overhead service drop, with a distance of maybe 100 feet between the Transformer(s) and the actual point of demarc for the Utility company (this would be where the utility's feeders terminate to the Service Entrance feeders).
The distance + the small size of the overhead feeder conductors on the utility side, reduce the available fault level down to maybe 5KA maximum, at the point of demarc.
Additional Impedance of the Service Entrance conductors, plus the Service Disconnect device, brings the available level down to maybe 4.5KA maximum.
Add the possible 1KA fault level of the Reactive items to the possible 5KA at the Service, and the available SCA is less than 10KA.
If the AIR of the Service Equipment + Devices is at least 10K, the system is compliant.
This is what would be found on individual small commercial type offices - like upto 2,000 sq, ft. and only HVAC Motor loads.
When feeders sizes are larger, &/or in multiple, Transformers are larger, closer, low % Z, Service Capacity is large (800 Amps and up), Motor loads are > 10 KVA; the available fault level is much greater.
That's all for now!
Let me know if you would like additional information.
Scott35