I was at work today (over the summer I'm working at an ice cream store) and I noticed that the LV (MR16) fixture (an open bottom recessed can) over the waffle irons was giving only 10% (roughly) of it's normal light output. All the other fixtures on the switch and circuit are operating normally. Two questions result: could the steam given off by the waffle iron be affecting the output (perhaps shorting the HV leads on the transformer), and are there any suggestions on fixes for this problem? Thanks y'all.
|
|
|
|
Joined: Dec 2005
Posts: 141
Member
|
changing the lamp would be a good start.
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
Assuming thay a new bulb will also be just as dim.... then the problem is likely in the wiring.
Since it is just the one light, the best guess would be a bad splice or connection.
Low voltage lights are powered by transformers with very limited power output. Other causes of dim light(s) I have found have included: -too much voltage drop, caused by too long of a wire; -too many lights n the transformer; and, -different circuits (some power supplies have more than one output circuit) interconnected.
|
|
|
|
Joined: Jun 2006
Posts: 110
OP
Member
|
Thanks for the help. I went to try and change the lamp this morning, and it turns out the (inline) connector between the lamp housing and the LV transformer was arcing (there is a lead of wires, then a connector, then more wire; no idea why). At least, that's my guess based on how the connector was showing visible signs of over-heating-- brown, crumbling, and slight distortion (one piece fell off in my hand as I went to break the connection). The connector will be replaced, but I want to figure out why this happened and how to prevent it from happening again. Not really necessary to keep replying, but I do appreciate you guys helping me figure out where to start.
|
|
|
|
Joined: Dec 2004
Posts: 209
Member
|
I believe the connector is to make it easy to change the low-voltage socket. I usually keep 4 or 5 sockets with me as I find many problems with them. Seems the halogen lights burn real hot and when the connection gets weak, the wire fries.
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
"why this happened and how to prevent it from happening again"
Tight - solid, and clean connections.
The amperage of the connections on the low voltage side of the transformer are 10X's what they are on the line voltage side. (.417 vs. 4.17) A loose connection will heat up, arching more and more over time and eventually fail.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Jun 2006
Posts: 110
OP
Member
|
That's the funny part-- the connector that failed was pre-installed in the fixture. Could be when it was installed we forgot to check internal connections, though (making a mental note for next time).
|
|
|