0 members (), 483 guests, and 9 robots.
#66453 06/04/06 01:54 PM
Anybody know the catalog # of a 100 amp breaker that goes in those GE panels that have the 1/2" THQP breakers? I didn't take the panel off tho look at the buses. I looked at the THQP's at Homedespot and noticed the tabs are a bit different than the regular snapins and the THQP's only go up to 50 amp.
#66454 06/04/06 03:00 PM
Are you looking for a main breaker or a branch-circuit breaker?
Larry Fine
Fine Electric Co.
fineelectricco.com
#66455 06/04/06 04:01 PM
Branch
#66456 06/04/06 04:37 PM
O
THQL21100
#66457 06/04/06 09:31 PM
Larry Fine
Fine Electric Co.
fineelectricco.com
#66458 06/04/06 09:35 PM
You are correct that the highest amperage in a 2-pole, 1/2-size THQP breaker is 50a (THQP250).
Larry Fine
Fine Electric Co.
fineelectricco.com
#66459 06/04/06 10:17 PM
F
Larry :
I did double check the master catlog book with me and yes it is correct the half inch verison is 50 amp top [ THQP250 ]
but for one inch verison it go much higher 125 amp max after that it go " 4 breaker verison " it will top at 200 amp
Merci , Marc
