ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 4 1 2 3 4
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
In an existing building the utility is replacing transformers (for an addition which will have a new separate main disconnect). The new transformers have a much higher short circuit let through current. The original building service is a 50 year old ITE switchboard.
The let through current is over 80,000A.
The short circuit rating of the main circuit braker is 50,000A. (the transformers are about ten feet away from the switchboard indoors in a room next to the electric service room)
Any suggestions (other than replacing the entire switchboard)??? The main circuit breaker and switchboard are rated at 1600A.

Joined: Dec 2003
Posts: 751
E
Member
http://www.ferrazshawmut.com/products/pdf_107/A4BQ.pdf

try current limiting fuses in a appropriate enclosure between the transformer and the main.


Earl
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Anything put between the transformer and the existing equipment would have to have a tested series rating. It is all but impossible to get a calculated series rating unless the existing equipment are "power circuit breakers".

Have you thought about running the incoming cables around the building a few times? This will add impedance and lower the available fault current.

Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
You only have a few choices. By mearly adding a current limiting device between the transformer and the 50kAIC breaker doesn't help. They must be series rated together, which they generally are not for older equipment.
You can add a reactor downstream of the transformer, and it will limit fault current, but be careful of voltage drop problems.
Validate the fault current that you are being told, at least with an infinite primary calculation, and don't forget to add contribution from downstream motors.
Wire can reduce current significantly, so run lots of wire as mentioned by JBD.


Ron
Joined: Jul 2004
Posts: 625
S
Member
Tie the wire in a knot. [Linked Image]

Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Is the transformer something close to 3750kVA with a 480V secondary?


Ron
Joined: Jun 2004
Posts: 1,273
T
Member
The Circuit Breaker can be the first or second element in series....

Install L or T type current limiting fuses with an appropriate rating: have an EE design it.

If the bussing permits, install a different breaker.

With such an old piece of gear: scrap it.... (I can't believe that old breaker is still passing its tests.)

Alternately, feed the existing service from the new installation. Re-engineer it.

Blame the extra on the Poco. Not your fault.


Tesla
Joined: Sep 2003
Posts: 650
W
Member
Perhaps you could just run each phase in its own conduit.... (*ducking*)

-Jon

Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Jon,
That would help, but be sure that PVC conduit is used.


Ron
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Check the fault current as given. If you were given a fault current with an infinite source the actual value will be less. You will need to recaculate the fault including the utiltiy system impedance. The utility may be reluctant to give this information.