Was curious to know if (2) soda machines set in the middle of a room could be wired with flexible cord attached to a twist-lock receptacle attached to the ceiling grid of a suspended ceiling. Would 400.7 (A)(6) cover me?
|
|
|
|
Joined: Jul 2005
Posts: 46
Member
|
Also take a look at 422.16(A)
Chris
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
They may want some independent support of the box. Running an extra support wire or two should calm that fear.
Greg Fretwell
|
|
|
|
Joined: Aug 2001
Posts: 16
Member
|
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Shock: 'Cord' cannot be used for permanent wiring methods. That said, IF you have a vend with a cord long enough to reach your receptacle, no problem.
IF you are proposing a twistlock to cord to a 1900 box that the machine cord will plug into; that does not fly.
Dependent on the ceiling height, you may want to consider a power pole, or IMC/RGC from ceiling to floor with the recept(s) installed therein.
John
John
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
By the way vending machines require GFCI protection if integral or by the branch circuit.
2005 - 422.51
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Sep 2003
Posts: 650
Member
|
Hotline1:
Wouldn't a permanently installed cord hanging from a box to a female cord cap be explicitly permitted by 400.7(A)(1)?
-Jon
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
Perhaps I missed what he was trying to do. I was thinking the receptacle was in a box, attached to the grid and it was connected with an article 300 wiring method above the ceiling (MC whip or something).