516
17
What do you like to use to splice the service entrance cable to the utilities service when doing residential service changes. Here the utility company can take up to 3 weeks to change a service over but we can make the connections and they will reconnect them later when they descide to show up. Remember you are doing this hot.
I have seen split bolts, set screw inline splices, crimps, insulated splice blocks, insulated terminal blocks and, ( are you ready for this one ) NM connectors, with or without tape. Connectors are not returned or left at the job site so expense [ as always ] competes with safety. Alan--
I like the Polaris insulated connectors for the hots. I think they are about $15 each. A split bolt for the ground. If I had a crimper that would be my 1st choice.
Burndy Crimps!
I used to work for a guy who would have us use 3/4" romex connectors.
You guys do this out of a bucket? Can't imagine doing it off a ladder.
If I never get to reconnect a service drop, I won't regret it. Those of you who do it, what precautions do you take? Does anyone meg out your entrance conductors first? That probably sounds excessive, but the idea of a 10kA fault occuring a foot from my face while I'm twenty-five feet up a ladder, is enough to make me pause.
=John
Walrus, we do it both ways. Off ladders, in a bucket, off the roof, the bucket is easiest...
John, we do a tap test. Tap the wires together before you hook them up....
Dnk...
[This message has been edited by Dnkldorf (edited 02-14-2006).]
Dnk, that's the "tapas turn" test right? tap as you turn your head