ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 474 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#61255 01/20/06 08:27 AM
Joined: Mar 2005
Posts: 49
S
sandro2 Offline OP
Member
A 200 amp residential service with the Pipe installation inside of the home?
-needs to be encased in concrete
-Can the pipe be EMT?
-Also what is the disconnect rule as far as the distance of the pipe before installing a disconnect

#61256 01/20/06 11:16 AM
Joined: Sep 2004
Posts: 37
E
Member
Y dont u use pvc if u going 2 encase it in concrete.

#61257 01/20/06 11:55 AM
Joined: Jul 2005
Posts: 46
R
Member
If you are talking about the service entrance conductors, then you must meet the requirements of 230.6 to be considered outside of the building.

EMT can be installed in concrete if 358.10(B) is meet.

230.70(A)(1) says "inside nearest the point of entrance of the service conductors." Only the AHJ can determine what is "nearest the point of entrance." Some AHJ have allowed 5 feet but you will want to check with your local AHJ.

Chris

#61258 01/22/06 05:54 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
This is one of the widest varying regional items around. Some AHJ allow nothing inside, some allow no encasement for 40'+! Really depends on where you are, and what is allowed there. This is definatley a question for your local inspector, and POCO.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#61259 01/22/06 12:48 PM
Joined: Feb 2005
Posts: 361
C
Member
My AHJ will allow 5' inside...I have a situation where I need 8' and I don't want to put in a meter main stack. The AHJ will allow my installation ONLY if the entire load side of the meter is RGC ~ no concrete required.

You will get varying details from people.

Your best bet is to ask the AHJ that is inspecting (another AHJ - even if the same jurisdiction - *might* not allow what the other agrees to).


~~ CELTIC ~~
...-= NJ =-...

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5