279
15
Had this prob in one of our schools yesterday, opinions welcomed: One of our new electricians installed a multiwire ckt (3 wire/shared neutral) out of a "computer only" panel (208Y120) to run two circuits for 2 identical laminators. These machines are identical. They run on 120v, have a small motor (about 1 amp) and a heating element (about 5 amps), that's it. When he plugged them in both would run the motor but as soon as he turned on the heat, they shut down internally (popped the reset). Never tripped any breaker. He tried: 1) Turning off one breaker so the neutral was not shared. 2) unplugging one machine. Regardless of what he did, neither machine would run. As soon as he plugged them into a recep from another panel both worked fine. Background: The computer panel is not in the comp room, it's on the other side of a block wall. He does not know what type of xfmr is feeding the panel but I suspect it's an "el cheapo" not a K. Two wire circuits gave the same prob when run from this same comp panel. There were no reported probs on the computers during his testing time. Voltage to neutral and ground read normal. All of us school board electricians are doing what we do best here ... drinking coffee, eating donuts and scratching our heads. Any thoughts?
[This message has been edited by Steve Miller (edited 01-20-2006).]
I'll take a stab. Voltage to neutral and ground read normal. Was the voltage reading taken at panel or point of use? I am wondering if the UPS system for the computers might be "masking" a neutral issue?
Here is a SWAG. Because the internal overloads tripped and not the breaker I tend to think that the circuitry is ok the issue is with the amperage to the units. Low amps causing the motor or heater to enter an overload situation due to insufficant amps. Beacuse the amp draw is so low it will not cause enough resistance heating to trip the breaker if it increases gradually. If you get 120 v line to neutral we know that the path is intact less the load. Let us consider some limiting factors that could limit the amp draw throught the circuit. The first thing that comes to mind is poor connections in J-Boxes or loose connections at the breakers or neutral bar or a bad receptical which is limiting ampacity.
What is feeding the "Computer Only" panel? I'm might be willing to bet it is an active UPS.
The rapid rise in voltage of a square wave, which is what most UPSs deliver to their loads, versus that of a regular sine wave, might cause the current to rise in your laminator unusually fast. When you add the fact that the resistance of the heater will increase as it gets hotter to the rapid rise of the current from the square wave, you might just be presenting enough of a shock load to a cheap reset for it to think a "short" has occured.
Just a thought...
[This message has been edited by Rick Kelly (edited 01-20-2006).]
Well, I see the obvious answer in Steve's original post big as life. You're trying to run laminators from a computer only panel! Of course they won't run!!
OK - seriously - this is a mystery. Here's a really long shot which should have no impact anyway, but is there even the smallest slimmest possibility that the new electrician wired the two new receptacles with H & N reversed? It shouldn't make any difference but you never know. Nothing else makes much better sense, and it's worth checking (descretely).
Other than that it would be interesting to hook up an oscilloscope to see what happens to the sine wave when the heater turns on. Try it using both the computer only panel and the other panel you mention (the one that works). It sounds like the laminator is causing the power supply at the panel to behave badly and then reacting to that by tripping the reset.
Radar
It could also be that the power supplies in those "computers" connected to that panels are sub-standard and you have loads of harmonics that are causing weird neutral to line currents. I would do a power survey on the panel to see how clean the feed is.
Would it be possible to check it with a megger? Could there be a leak in the insulation that would only be enough to pop the reset but not the circuit breaker?
In no particular order: The guy who wired the panel is new to us, not to electricity. H & N are correct H to N reading was taken at point of use. There is an UPS system involved and Rick's "square wave" theory seems to be a definite possibility. No chance of a megger. I think the next step is for me to get a scope and take a look. Thanks
Check that feed to the "computer only" panel.
Is it possible that the "computer Only" panel is fed from a power conditioner? And that is backed up?
Either way, you say it works fine when you plugged it in to another receptacle?
You'd have to give us some more info I'm afraid, tell us what you find?
The reset, is that a thermo built in the motor?
Dnk...
[This message has been edited by Dnkldorf (edited 01-20-2006).]
CDS
Nicholson Ga