1 members (Scott35),
542
guests, and
43
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Nov 2004
Posts: 53
OP
Member
|
What exactly is required when mixing voltages, ie. 208 & 277 in the same J-Boxes and conduits. As far as labeling, color codes etc. I know what is preferable, but what is required by code. Thanks in Advance.
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
They need to be separated by a non-conductive barrier.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
No barrier is required unless two devices in the same box have more than 300 volts between them.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
.....And at least one of those devices is a snap switch
|
|
|
|
Joined: Nov 2005
Posts: 827 Likes: 1
Member
|
Don't all of the conductors have to have an insulation rating appropriate for the highest voltage used? Joe
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Yes, they do. All of the Building Wire that I'm accustomed to working with has insulation rated at 600V, so it would qualify for highground's original query.
Now my question: What is the insulation rating of Cat5/Cat6 etc. cable? How about Bell Wire/Thermostat Wire?
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
Now my question: What is the insulation rating of Cat5/Cat6 etc. cable? How about Bell Wire/Thermostat Wire? Most CAT5/6 I've seen is rated at 300 volts. I'll check back on the new CAT6 I just used on a job, it's in the warehouse... I've seen t-stat wire at both 150v and 300 volts. Not sure about bell wire. Anyone? Anyone? Bueller? Bueller?
Stupid should be painful.
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
What exactly is required when mixing voltages, ie. 208 & 277 in the same J-Boxes and conduits. As far as labeling, color codes etc See 210.5 in the 2005 NEC. Don the code section should be 210.5(C) [This message has been edited by resqcapt19 (edited 01-19-2006).]
Don(resqcapt19)
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
What is the insulation rating of Cat5/Cat6 etc. cable? How about Bell Wire/Thermostat Wire? Then you have to look at 725.55(A). Even if the communications and controls cables have a voltage rating higher than that of the power conductors, you still can't mix them in the same raceway. Don
Don(resqcapt19)
|
|
|
|
Joined: Jan 2005
Posts: 74
Member
|
725.55(D) allows for mixing voltage class wires so long as the class 2 wires pertain to a device in that box. A nice one for lighting control systems.
|
|
|
Posts: 524
Joined: December 2003
|
|
|
|