ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 560 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Joined: Aug 2004
Posts: 55
W
wendel Offline OP
Member
Rather than a copper-clad steel rod, is it acceptable to use an 8 foot piece of 3/4" copper pipe (driven into the ground) as a ground rod? Is there a requirement that the grounding rod be solid or is that to make it easier to hammer it into the ground?

Joined: Jan 2006
Posts: 69
W
Member
Thats a good question I would say yes because it would be the same as using the water supply as a GE. but some one will probably prove me wrong.


Thanks.
Joined: Aug 2001
Posts: 16
G
Member
It would probably have to be listed for the purpose

Joined: Jan 2006
Posts: 69
W
Member
see what did i tell you. lol
geno, makes a good point. it would have to be listed for that purpose.

[This message has been edited by Wizzie Electric (edited 01-17-2006).]


Thanks.
Joined: Dec 2005
Posts: 152
A
Member
Two words: "Not listed". However......

Stick an old gate valve and solder a copper 90 on to the end of it so that it technically becomes part of the water supply system and VIOLA, its acceptable.

See we all thought plumbers were out there to make life difficult, and as it turns out [Linked Image]

Joined: Nov 2000
Posts: 2,148
R
Member
Look at 250.52(A)(5). There is no requirement that a pipe used as a grounding electrode be a listed product.
Don


Don(resqcapt19)
Joined: Aug 2004
Posts: 55
W
wendel Offline OP
Member
The only physical requirement for a copper ground rod I can think of is that the volume of copper per inch in the grounding electrode be equal to or greater than the volume of copper per inch in the connecting/bonding wire. Otherwise a surge current could generate enough heat to melt the electrode while the connecting wire was still intact. Unlikely, but we're talking hypothetical extremes to help understand the right way to do things.

Joined: Oct 2003
Posts: 172
G
Member
I would be worried about corrosion as the intent of the copper pipe was not to be buried.

Joined: Mar 2005
Posts: 1,803
Member
If youre going to pretend it's plumbing (by nailing an old gate valve on top), it needs:-
a] to be at least 10 feet long.
b] an additional earth driven rod too!- see 250.53(D)(2)

Alan


Wood work but can't!
Joined: Nov 2000
Posts: 2,148
R
Member
wendel,
Quote
The only physical requirement for a copper ground rod I can think of is that the volume of copper per inch in the grounding electrode be equal to or greater than the volume of copper per inch in the connecting/bonding wire.
The code does not contain any such requirement. 250.52(A)(5) permits the use of any metal pipe at least 8' long and with a minimum size of 3/4" to be used as a grounding electrode.
Don


Don(resqcapt19)
Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5