ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 248 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#60916 01/13/06 05:46 PM
Joined: Jun 2005
Posts: 73
W
Member
Hi everyone. I have been having some problem with some 2x4 troffers. Customer called last week a bunch of fixtures are out I changed 6 of the ballasts. a few days later they tell me the breaker keeps tripping so I put my amp meter on it it was pulling 24a so I split the circuits instead of 2 circuits now there are 4 for all the lights. I come this morning I see 2 ballasts are out one is one I just changed. What am i looking for?

#60917 01/13/06 06:00 PM
Joined: Oct 2004
Posts: 806
Member
Need more information to really help..how many fixtures were on each circuit, is the panel serving them 3 phase, were the circuits sharing a neutral?

Shared neutrals are a big no-no with ballasts, especially electronic ones. Harmonic currents add up rapidly and cause no end of problems and repeated ballast failures.

And any loose connections can kill e-ballasts rapidly. Had one case personally where we went through 3 ballasts on the same fixture until I pulled on the whip and the loose wirenut fell off in ther j-box. Fixed that and no more failures since (about 6 years now.)


Stupid should be painful.
#60918 01/13/06 06:29 PM
Joined: Jun 2005
Posts: 73
W
Member
about 20 lights per circuit. single phase service. lights are fed from a 3 wire circuit.

#60919 01/13/06 06:40 PM
Joined: Jun 2005
Posts: 821
S
Member
That shared neutral is doing twice the work of either of the ungrounded conductors. IMO you need to install a dedicated circuit and split up the fluorescent lighting.

Good luck!

#60920 01/13/06 08:06 PM
Joined: Nov 2002
Posts: 794
Likes: 3
W
Member
Quote
single phase service

That shared neutral is doing twice the work of either of the ungrounded conductors.

If it's single phase (pair of 120Vs 180 degrees out of phase) electronic ballasts on both sides should be drawing their spikes of current at the same time (in respect to the timing of a 60 cycle waveform) and thus the neutral should be sharing/splitting the spikes the same way it would if the loads were just resistors. When you get neutral overload is when you have multiple phases, 120 degrees out of phase. Then the loads on phase A draw their spikes of current at a different time then those of phase B.

A bad connection on a neutral could cause problems like those you normally see with neutrals serving other kinds of loads.

[This message has been edited by wa2ise (edited 01-13-2006).]

#60921 01/13/06 08:54 PM
Joined: Jun 2004
Posts: 220
T
Member
20 ballasts per circuit? check the amount of current each is pullin, it can add up. As long as they are not on the same phase, the neutral in the 3wire circuit should only have the imbalance on it, if they are on the same phase, the current in the neutral will be the sum of the current on both phases.

#60922 01/13/06 11:51 PM
Joined: Jan 2002
Posts: 70
Member
Are the right lamps being used. Maybe too high a wattage for the ballast.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5