ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 390 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#6041 12/20/01 07:28 AM
Joined: Dec 2001
Posts: 50
J
Member
A 4 wire 3phase system with 480 volts phase to phase and 277 volts phase to neutral. Is this always a wye system? What are the differences between 480 Wye systems and 480 Delta Systems?

Thanks

#6042 12/20/01 07:44 AM
Joined: Oct 2000
Posts: 2,749
Member


Joe Tedesco, NEC Consultant
#6043 12/20/01 08:00 AM
Joined: May 2001
Posts: 717
G
Member
Joe, The short answer is, a Delta system will produce phase to ground voltage that is 1/2 of the phase to phase voltage, Wye system the phase to ground voltage is phase to phase voltage X 1.732. In your question 480 X 1.732 = 277, therefore you have a Wye system. Let's make that 3 phase systems, single phase transformers can be wound in any danged way ya wanna.

#6044 12/20/01 01:28 PM
Joined: Nov 2000
Posts: 2,148
R
Member
If the voltage to ground is 1/2 the phase to phase voltage, you would have a 4 wire delta with a high leg. If the delta is ungrounded the phase to ground voltage will float between 0 and the phase to phase voltage. If the delta is a grounded delta, one leg will be 0 volts to ground and the other 2 will have the phase to phase voltage to ground.
Don(resqcapt19)


Don(resqcapt19)
#6045 12/20/01 07:38 PM
Joined: Dec 2001
Posts: 37
A
Member
The delta connection of the circuits in a three phase system in which the terminal connections are triangular like the greek letter DELTA. The delta connection will stand 1.732 as much current as the Y connection, but will give only .577 as much voltage. 480 X .577 = 276.96
(NOT) 480 X 1.732 = 831.36

#6046 12/20/01 09:18 PM
Joined: May 2001
Posts: 717
G
Member
OOPS 480/1.732 = 277 fat fingered, non-proof reading rascal.

#6047 12/21/01 12:55 AM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Joe [Joe Carpenter],

Are you looking for Schematics, or technical differences between Deltas and Wyes?

If you would like to view some Schematics, look in either the Technical Reference area or the Electrical Theory area of this forum [ECN]. I'll post hyperlinks later if needed.

I'll add some tech data later on.

Scott SET

P.S. Does anyone manufacture a 480/277 4 wire Tee Transformer???

SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5