ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 219 guests, and 9 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#60199 01/11/06 07:09 AM
Joined: Dec 2005
Posts: 869
Likes: 4
R
RODALCO Offline OP
Member
Just came back from streetlight patrol and I had to scope a problem where lights had failed, but on a important intersection.

After opening at least 10 pole and pillars the last one, overlooked in the beginning, was the culprit where a linetap had filled up with water from the dew in the s.l. pole and tracking caused leakage in the almalgamating tape then bang!!! short out to earth and loss of supply.
Fixed problem and re instated supply for the night. I put the s.l.'s on 24 hours supply from the transformer, because i did'n feel to interested to open probably an other 10 or so pillars and get eaten by the mossies at the same time.
Of couse no schematics in a new subdivision and NZ s.l. wiring is far from logical.
The load here was only 7 Amps @ 230 Volts.

BTW
Some circuits we have problems with run at 35 Amps through 10 mm² cable for about ½ kM.
You can see that the volts drop will cause low voltage at lamps or burn out from poor connections.


The product of rotation, excitation and flux produces electricty.
#60200 01/11/06 07:11 AM
Joined: Dec 2005
Posts: 869
Likes: 4
R
RODALCO Offline OP
Member
Just came back from streetlight patrol and I had to scope a problem where lights had failed, but on a important intersection.

After opening at least 10 pole and pillars the last one, overlooked in the beginning, was the culprit where a linetap had filled up with water from the dew in the s.l. pole and tracking caused leakage in the almalgamating tape then bang!!! short out to earth and loss of supply.
Fixed problem and re instated supply for the night. I put the s.l.'s on 24 hours supply from the transformer, because i did'n feel to interested to open probably an other 10 or so pillars and get eaten by the mossies at the same time.
Of couse no schematics in a new subdivision and NZ s.l. wiring is far from logical.
The load here was only 7 Amps @ 230 Volts.

BTW
Some circuits we have problems with run at 35 Amps through 10 mm² cable for about ½ kM.
You can see that the volts drop will cause low voltage at lamps or burn out from poor connections.


The product of rotation, excitation and flux produces electricty.