#6020 12/23/01 07:04 PM
Joined: Aug 2001
Posts: 151
D
Member
Just to throw another fly into the ointment, most if not all mounting methods for EGC terminal bars use a set of self-tapping screws that tap into pre-punched holes in the panelboard cabinet back. So are some here saying that this technically isn't NEC compliant?

The difference between self-drilling, self-tapping, and plain ol' sheet metal screws seem pretty clear, in both definition and the graphics above. There are numerous places where the Code seems to expect us to use logical reasoning beyond the written portion of the Code

Dallas

[This message has been edited by Dallas (edited 12-23-2001).]

#6021 12/23/01 09:23 PM
Joined: Nov 2000
Posts: 2,148
R
Member
electure,
I was speaking in reference to my earlier post that said "if I was an inspector...".
As far as the interpretation, I am looking at the words in the code as well as the comments in the ROP and ROC. The CMP has "screwed up" here. The words used say we can only use listed means and therefore standard screws are a violation. This section needs a revision to make it enforceable. The sheet metal wording was never needed in 250.8 as sheet metal screws are not a listed means of connection. I will be submitting a proposal for the 05 code.
Don(resqcapt19)


Don(resqcapt19)
#6022 12/24/01 08:03 AM
Joined: Dec 2000
Posts: 4,294
Member
Agreed, Don.
The Code should have been written in a more positive manner, rather than excluding anything as generic as a sheet metal screw. Any screw that is screwed into sheet metal could be construed as a sheet metal screw.

I think, though that if an inspector called me on having a good, solid machine screw used as a ground, and wouldn't let me off with 90.4, I would be inclined to whip out my box of crummy Ground Clips, show him the little UL stamp on each one, and exclaim "How do you like me now?" I think this would make an inferior connection as opposed to the first one.
I see on a daily basis Tek screws, toggle bolts, plastic anchors, drywall screws, and the like with ground wires shoved under them. I think the Code's intent is to provide a solid termination that won't come loose, and is used solely for the purpose of grounding.