Electricians revenge
1 members (Scott35), 128 guests, and 12 robots.
#59957 12/19/05 11:21 PM
BigB Offline OP
Has anyone wired for a mini split? I have to rough in for a 1 ton. I was wondering if the indoor unit is powered by the connecting cable that runs from the condensing unit to the blower or does it require a circuit of it's own? It is a GE unit.
thanks...
#59958 12/20/05 08:01 AM
The ones that I've wired...not GE... have taken a common supply circuit. As a matter of fact, they have had full voltage controls.
Your answer should be in the installation instructions.
#59959 12/20/05 08:23 AM
Electure,
I've wired Carrier and various other brands.
As far as I'm aware (out on a limb here) A/C units use a 5 core cable between the Evaporator and the Condensor unit, size of wire 1.5mm2 in my language.
The load is usually only a fan motor and few control circuits at the Condensor end.
Allow 8 wires, I will say this.
#59960 12/20/05 11:50 AM
As already stated here, best bet is to get a hold of the installation literature.
#59961 12/20/05 09:51 PM
I have wired a couple recently that were fed with a 15 amp 120v circuit to the outdoor condensor unit. The indoor fan unit was powered by 36v dc supplied from the outdoor unit via a 4 wire 18awg cable.